Page 1 of 2 12 LastLast
Results 1 to 13 of 20
  1. #1
    Join Date
    Aug 2000
    Location
    Austell, Ga.
    Posts
    1,306
    Post Likes

    York YK Impeller Eye and Balance piston wear.

    First off please allow me to preface this post with the fact that I have done dozens of YK repairs with both R-22 as well as the R-134 versions.
    Many of these repairs were in the warranty period and some with less than one month run time. I no longer work for the "Big Blue" conglomerate and feel that the response I was given years ago to the problem that I should, "Keep my mouth shut" no longer frightens me...Here goes guys...

    As you should be aware, all the YK's(YT's) rotate the impeller Counter-Clockwise facing the Impeller inlet.
    "ANY" YK compressor you take apart "Will" have impeller damage with the majority of the wear from impeller grooving from "Both" the Eye seal and Balance piston at the 10-11 O-clock position..The ones with VSD's do show as much damage as the units with DOL or Wye-Delta start.I am certain that others has seen this but have possibly overlooked the source of the problem.
    Relax and just visualize what can possibly "Push" the impeller towards the 10 O'clock position....It ain't gonna' happen now is it...Therefore the spring loaded Impeller eye seal (Forget the balance piston now) "MUST" be coming down towards the 5 O'clock position to cut such grooves in this pretty wheel. The Impeller labyrinth has very deep grooves cut into it and can store a certain quantity of oil-refrigerant mixture in these grooves...As the compressor is started this area takes a sudden and and deep pressure drop to the point that the oil-refrigerant mixture "Cannot" exist in this liquid state and as the refrigerant now Expands to almost 1000 times it's area forcing the oil to seal further expansion and literally drives the Labyrinth into the impeller at the 10 O'clock position. The more starts, the deeper the impeller is grooved, the more oily mixture, the better the seal, the greater the force applied on the next start to only deepen the "Grooving" of the once pristeen impeller.

    The solution....Simple enough to one who has seen the internals of waaaay' to many Carrier centrifigals. and that is to simply drill a very small hole (1/16th or smaller) on the labyrith seal thru the grooves at the 6 O'clock position. This "Will" allow the oil-ref mixture to drain from the seal eliminating the pushing of the seal and balance piston into such a lovely impeller.
    I took it on myself to this on a few compressors before I left the "Big-Blue" fiasco and will be curious as to what the guy who takes them apart someday will think when he sees the lil' hole....I am absolutely certain tho' that unless he has major bearing wear he will NOT see Impeller Grooving...
    I only hope that this post is recieved in the intent that it was posted...
    Ain't "None" of us as smart as "All" of us..

  2. #2
    Join Date
    Sep 2007
    Location
    Somewhere in the world.
    Posts
    1,683
    Post Likes
    Richard that is an excellent explaination thanks for sharing that information with all of us I am sure that it will be well percieved for future reference.
    A mind is like a parachute. It doesn't work if it is not open.

    The best part of going to work is coming back home at the end of the day.

    Hard work spotlights the character of people: some turn up their sleeves, some turn up their noses, and some don't turn up at all.

  3. #3
    Join Date
    Oct 2003
    Location
    tidewater, va
    Posts
    2,154
    Post Likes
    richard you are the man

  4. #4
    Join Date
    Nov 2006
    Location
    North Carolina
    Posts
    134
    Post Likes
    Richard,

    Did you drill a hole in between each groove or just 1 hole in the middle on the seal? Great explanation!

  5. #5
    Join Date
    Aug 2009
    Location
    Taiwan
    Posts
    63
    Post Likes
    Hi Richard,
    Some B.P Seal photos that can proove your viewpoint,
    these photos I took from the compressor that I asked for your help by mail months ago,
    I did drill a 1/16" hole on the center of the ring, hope I can have chance to check it again.

  6. #6
    Join Date
    Aug 2000
    Location
    Austell, Ga.
    Posts
    1,306
    Post Likes
    I'm sorry I was not clear in what I think is a solution to a problem that has plagued the Yorks for years. What I have done is to drill all the way thru the grooves (1/16") at the 6 O'clock position with the hole just touching the bottom of the grooved area thereby allowing any mixture of oil/ref. to drain during shutdown.
    There is "NO" way that a hole that small, away from the labyrinth sealing area could detract from the sealing effect provided by the seal/balance piston.
    I want to thank one and all for not flaming my post, as I truly expected to be assailed by one and all for my attempt at helping others with my view on this...
    Taicool....You are one brave soul my friend, to even attempt making such modifications on the word of this lowly scribe...But.....If the seal(s) you modified ever wear "Without" a major bearing failure.....I will chip in on the cost of repairs...Great to hear from you again Tai....
    Just wait until I post my findings on the York "J" and "Z" compressor wipeouts...
    Ain't "None" of us as smart as "All" of us..

  7. #7
    Join Date
    Sep 2011
    Location
    Northwest Louisiana
    Posts
    317
    Post Likes
    Thank you Richard for this information, I too have opened many Yks and found nose damage to wheel. When with York I questioned engineering about this grooving of wheel, D.D. advised that since nose seal is "floating" the damage occurs on the first start-up as the wheel centers the seal and not to worry about it. I beleive your explaination is relavant and will drill that hole on our next overhaul.
    A LITTLE BIT OF STUPID GOES A LONG WAY!

  8. #8
    Join Date
    Jun 2012
    Location
    so cal
    Posts
    22
    Post Likes
    wow i think i found the answer i was looking for

  9. #9
    Join Date
    Aug 2009
    Location
    Taiwan
    Posts
    63
    Post Likes
    Richard,
    I am not the brave one,
    before I did that, I have conveyed the information to a master in the refrigeration field in my country,
    in his 30 years career he has a lot of experience on repairing York centrifugal compressors, he totally acknowledge your view.

  10. #10
    Join Date
    Aug 2000
    Location
    Austell, Ga.
    Posts
    1,306
    Post Likes
    Taicool;
    I am deeply humbled that you as well as the master you referred to would consider the opinions of a one time service man.
    I am now retired with my local union(LU72) and am presently working as a maintenance man at a local data center working on lawn sprinklers, changing filters ect. As I absolutely refused to buy into the Johnson Controls Next-Gen methodology of doing service and repairs I chose to leave before I was asked to. I deeply envy and respect those guys behind the windshields of thier service trucks, regardless of company, catching service calls and actually fixing things. In other words...I truly miss the hunt...I guess I am too old to pull the chains any longer and I never learned how to push one. The high point of my day now is this web-site as I look forward to reading the verbal sparring of the likes of Jayguy, Dallas Duster and others. I fear entering the battle of wits these guys use....for I have no weapon in such a fight...
    Ain't "None" of us as smart as "All" of us..

  11. #11
    Join Date
    Nov 2006
    Location
    US
    Posts
    112
    Post Likes
    Ok, here it goes i lost sleep over this. I have to ask why is that liquid and oil getting to that high area in machine. I dont recall seeing much oil in any eye seal. also expansion would take the path of least resistance therefore wouldnt gas go all the way around grove and center seal before pushing seal in any direction. I dont see how pressure drop could happen fast enough to cause this (mini explosion). Dont get me wrong i do follow your logic but i have to reason it all out i my head.

  12. #12
    Join Date
    Nov 2006
    Location
    US
    Posts
    112
    Post Likes
    wha was eye seal run out on these machines and why were they opened?

  13. #13
    Join Date
    Aug 2000
    Location
    Austell, Ga.
    Posts
    1,306
    Post Likes
    There was a period of time a few years back where the vanes were not shimmed properly on many of the YK's being shipped and the ball end connector that drove the blades would "Pop" out of there lil' holes,and sometimes....they would "Pop" back in.(Leaving a distinct wear trail on the operating ring) I personally did the rebuild on six of them and replacing the entire vane assembly on one. Each and every one had wear, some extreme in the 10-11 O'clock position "Only", of the eye seal as well as the balance piston. On one of them at a local hospital, the wear was so bad we replaced the impeller due to the "Extreme" depths of the grooving.(X-line start) Mssr. DD sent a replacement impeller coated with a greenish teflon coating to try. Kinda' like the Westinghouse impellers of old. I later called DD and informed him it took hours for us to remove whatever coating that was....If one has never heard Brer' DD "Screech" over the phone you have truly missed out...I was only joking with him, but his tolerances of humor are truly limited.In each and every one of these mentioned the bearing clearances were perfect in every respect.
    Ain't "None" of us as smart as "All" of us..

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.
Comfortech 365