    anyone have info on how they work for damper actuators and why they are used??

  2. #2
    Join Date
    May 2004
    Location
    SE Pennsylvania
    Posts
    515

  3. #3
    Join Date
    Aug 2008
    Posts
    299
    cant see it. i do not have access to this forum....

  4. #4
    Join Date
    Sep 2008
    Location
    Cedar Rapids, IA
    Posts
    473
    Pilot positioners are used for two reasons. The most common reason is to adjust the spring range, ie the pressure at which the actuator is fully open or closed. I've seen them most often on steam line setups where there is a 1/3 capacity valve for fine control and a 2/3 capacity valve.

    The other reason is that you can get faster or slower movement because of the direct supply connection instead of going through a control device that might be volume limited.

  5. #5
    Join Date
    Aug 2008
    Posts
    299
    any one have a install guide for one??

  6. #6
    Join Date
    Apr 2012
    Location
    Paper Street Soap Company
    Posts
    2,294
    its a controller that acts as a assist to the primary actuator increasing branch pressure to overcome forces acting against the actuator.

    I use to see them on large actuators.

    It will have a main air line running to it.

    also if you dont know their function why are you installing one ?

  7. #7
    Join Date
    Aug 2008
    Posts
    299
    not installing one. just saw one and wondering how it works.

  8. #8
    Join Date
    Apr 2012
    Location
    Paper Street Soap Company
    Posts
    2,294
    ah..well there is your explanation. I see less and less pnuematics and pilot positioners.

    They're pretty nifty controllers in that you can use them to match spring ranges.

  9. #9
    Join Date
    Jul 2001
    Location
    Canada
    Posts
    1,710
    Here is a tech sheet that should help you out.

    http://www.cm3web.com/parts/pdf/F22909-7.pdf

    Still lots of them in use from all the major manufacturers

  10. #10
    Join Date
    Aug 2008
    Posts
    299
    thanks to all...

  11. #11
    Join Date
    Sep 2006
    Location
    Alaska
    Posts
    406

    Power

    I've seen people take out pilot positioners and the damper alone can't close or open a set of dampers. You can also use them to stage equipment by changing the start point and end point. For example you can put a heating valve and a cooling valve and stage them where the heat comes on from 3 to 6 psi and the cooling comes on from 8 to 11 psi, this also gives you a deadband from 6 to 8 psi where you have not heating or cooling.