It is spotless. Plate is smooth, no black anywhere, no scale deposits.
QD692N
010364563
Remote condenser.
Keeps locking out on excess harvest time. I clocked it today at 3 mins and 45 secs to drop. Makes a nice even sheet of cubes. The top of the sheet is coming off fine, the bottom isnt.
I adjusted the thickness probe and got it to drop in 3 mins flat. Thats too long. Its going to lock out again. Any ideas?
It is spotless. Plate is smooth, no black anywhere, no scale deposits.
Ugh, tech support? Thanks. Do they speak decent english?
http://icemakerpartsshop.com/article...c-ice-machine/
I checked this out once, and even checked the switch and counted the flashes, but it was the bin switch.
An evaporator can "look" clean, but it's always a good idea to give it a proper cleaning before attempting to diagnose a problem like this.
If cleaning fails to resolve it, this machine, being a Q-Series remote, has a harvest pressure regulator (HPR) which may (or may not) be a cause. Check your suction pressure during harvest. It should gradually climb to around 90 psig or so. If it stays down around 60-70, there's not enough heat going to the evaporator. Then it's time for a new one.
im with ice on this.. also check the weep holes on the plate.. those hpr system are tricky if your not fimilar..
Yes if you call tech support they speak english there located in Mainitowoc Wisconsin
Hell, the guy who you would speak with is on here, actually.
Oh JON BAILEY!!!!!!!!
Every customer you take for granted today will be someone else's tomorrow.
is it level..... lean it to the front...... I had a few with same problem... let gravity take over and all was well
it was working.... played with it.... now its broke.... whats the going hourly rate for HVAC repair
Remember to use your Manitowoc Service Tech Book. If you don't have one I urge you to get one. It has all the answers and makes troubleshooting faster and accurate.
Clean it!
Then time it. If it's still to long check the evap for loose plates. If that checks out I like to hold a flashlight against the plate and look for cracks where the plates attach to the back. What are your pressures in harvest?
Sent from my amazing 4G device
It was cleaned from top to bottom less than a year ago when I moved it from one store and installed it in another. The former store got a new in box unit that I installed as well.
About 2 months ago I get a call and they want me to come move it, that day. I couldnt make it that day so they called someone else to move it. I checked yesterday and the filter drier is the same one I put in when I installed it.
I generally dont even pull my gauges out of the truck on ice machine calls. I will today or tomorrow and check pressures.
Sorry for being late.. i need to check this site more often or set it up to notify me somehow.
There could be so many things wrong here, just not enough info. Do not be afraid to put your gauges on.
This what i need
Freeze pressures start middle and end
Harvest Pressures start middle and end
Hottest temp discharge line got in freeze
Temp of liquid line in freeze
Ambient Temp outdoors were condenser is
Freeze time?
Is compressor Body cold at end of freeze cycle?
Sorry for not responding sooner DLZ Dan!
Sorry for not updating. I was busy and they were screaming so I had them call my old teacher, who does refrigeration in his off time. I havnt talked to him but know when I showed up a few days ago to pull a clogged evap, the ice machine was full. Ill ask him what he found the next time we talk.
No problem. Would be interesting to find out.
Always inspect an evap when its dry. Even my dirty car looks good when its raining!