Hello looking for some help, this is my first post. From the past i would goggle the problem that i had and the answers always came from this site so i thought i would jump on board. I installed heatcraft m/n cht008x6bfm mid temp
Running on 404a and installed a new evap with the standard txv and solenoid last week. After running 2 days a got a call saying there was ice build up, the ice starts from the bottom and works its way up the coil over time,(not running a time clock). My pressures are 200/60 on 65 degree day with a 40 degree box temp. Seeing that everything is new I decided to turn up the tstat and make sure my unit pumped down and shut off on temp. After doing this my solenoid gets energized and seems to never close all the way leaving the unit running and never pumping down. Has anyone seen a new solenoid be bad.
Thanks
You got solder in it when you sweated it in.
Officially, Down for the count
YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET
I know enough to know, I don't know enough
Why is it that those who complain the most contribute the least?
MONEY CAN'T BUY HAPPINESS. POVERTY CAN'T BUY ANYTHING
I love the smell of phosgene first thing in the morning:
To apply for professional membership click here
Educational forums are open.
If you would like to submit a link or an article or other related info to the EF. click here
Snap it on and off a bunch of times.. Might clean it out. I would just pump it down from the king valve and take it apart and inspect it, clean it, or replace the guts if you burnt it up.
We had had a bunch of problems with Sporland solenoid valves not closing.. My company wont install them any more after like the 3rd one in a year. One of those was A flare valve too
I also had problems with new sporlan solinoids, I started oiling them when I put them together and have not had problems since.
Yeah I think there was some kind of service bulletin on the valves.
what is the low pressure switch set at? is the valve horizontal or vertical? if its vertical that could be your problem.i like to install mine horizontal.if its vertical when the solonoid deenergizes it might not be pulling all the way back in.
I see some of the new ones are coming with a little brass washer to help them close. Maybe there was a problem with them.