  1. #105
    Join Date
    May 2004
    Posts
    1,825
    Is it worth the extra bulk and stiffness to go with the 1/2" hoses over the 3/8" hoses??? 3/8 is a huge improvement over 1/4". Not sure if 1/2 would be enough advantage over the 3/8" to justify the added bulk.

  2. #106
    Join Date
    May 2010
    Location
    Canada
    Posts
    686
    Quote Originally Posted by 270wsm View Post
    Is it worth the extra bulk and stiffness to go with the 1/2" hoses over the 3/8" hoses??? 3/8 is a huge improvement over 1/4". Not sure if 1/2 would be enough advantage over the 3/8" to justify the added bulk.

    Depends on what size equipment you are working on.

  3. #107
    Join Date
    May 2004
    Posts
    1,825
    Mostly 5 to 15 ton. And I use a 6 CFM pump.
    Last edited by 270wsm; 01-10-2013 at 12:02 AM.

  4. #108
    Join Date
    Jan 2005
    Location
    Akron
    Posts
    977
    Quote Originally Posted by 270wsm View Post
    Mostly 5 to 15 ton. And I use a 6 CFM pump.
    1/2" For sure they are much faster than 3/8" I only use my 3/8" hoses for recovery.

  5. #109
    Join Date
    May 2004
    Posts
    1,825
    Ok so I'll go with the 1/2 inch hoses. Are 6' lenghts optimum, would going with shorter be better? Also, which 1/4 ends do you recommend, the straight or 45?

  6. #110
    Join Date
    Jan 2005
    Location
    Akron
    Posts
    977
    Standard 6' with straight fittings is what I use. It is a nice length that is easy to work with.
    JLB,

  7. #111
    Join Date
    May 2004
    Posts
    1,825
    I noticed my 3/8 brass tee doesn't really have a full 3/8 bore. Barely over 1/4 I.d. Are they all like that??

  8. #112
    Join Date
    Aug 2011
    Location
    Bangalore
    Posts
    21
    i am using 8 CFM vacumm pump & trying of vacummizing my 8.5 Tr unit having internal volume of around 1.8 cu.ft

    Ideally what should be the vacummizing time?? it is taking so long (around 7-8 hrs) to achieve 400 microns even.

  9. #113
    Join Date
    Jan 2005
    Location
    Akron
    Posts
    977
    Quote Originally Posted by 270wsm View Post
    I noticed my 3/8 brass tee doesn't really have a full 3/8 bore. Barely over 1/4 I.d. Are they all like that??
    Yes most are like that, however, it is the hoses that make the difference much more then the fittings. The hose creates a lot of friction that slows the evacuation. Flow is much different in a vacuum then in pressurized applications.
    JLB,

  10. #114
    Join Date
    Jan 2005
    Location
    Akron
    Posts
    977
    With the right hoses and the right process, i would guess less than 1 hour for sure. If the refrigerant is still out-gassing from the oil, it may take a bit longer, but not much longer than that,
    JLB,

  11. #115
    Join Date
    Feb 2013
    Location
    Huntsville, AL
    Posts
    76
    Is this really necessary though? I just put my regular gages and pump on every system I do and then do some other aspect of the install and come back to my pump and gage later, and it is always ready for me at below 500 microns and I have no wasted time of additional initial setup or the added expense the having to buy this kit.Anyone?

  12. #116
    Join Date
    Aug 2004
    Location
    North Richland Hills, Texas
    Posts
    14,914
    Quote Originally Posted by ComfortService View Post
    Is this really necessary though? I just put my regular gages and pump on every system I do and then do some other aspect of the install and come back to my pump and gage later, and it is always ready for me at below 500 microns and I have no wasted time of additional initial setup or the added expense the having to buy this kit.Anyone?
    On a new residential split system install, where you are just evacuating a linset and coil, it is usually massive overkill, especially with new copper lines.
    On repairs, where you have to evacuate the whole system, the time savings are very significant. A good evacuation setup can cut the time down to less than 1/3 the time it would take using your normal service manifold and hoses.
    On a large commercial system, you can save hours with a good evacuation setup.
    If more government is the answer, then it's a really stupid question.

  13. #117
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    24,946
    Quote Originally Posted by mark beiser View Post
    On a new residential split system install, where you are just evacuating a linset and coil, it is usually massive overkill, especially with new copper lines.
    On repairs, where you have to evacuate the whole system, the time savings are very significant. A good evacuation setup can cut the time down to less than 1/3 the time it would take using your normal service manifold and hoses.
    On a large commercial system, you can save hours with a good evacuation setup.
    I was thinking along these lines.

    If all that you do is new installation, then you could get away with just using a manifold by scheduling your work so that the pump has the maximum time to run. It isn't really the correct way to do it, but it would suffice.

    As Mark mentioned, though, there is more to the world than installing residential equipment. Sometimes, you're running a service call, replacing a compressor or even working on a larger system.

    I've switched to using 3/8" diameter hoses for pulling vacuum and, sometimes, I still work that old rhythm of install pump, fire it up, do the wiring, clean up my tools, set up the micron gauge, etc... It doesn't take that long, but when you're pulling a vacuum on freezer with a 2 5/8" suction line that's a couple hundred feet long, every bit of volume counts.

Page 9 of 10 FirstFirst ... 2345678910 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event