freezer/refrigerator
Servolift, Model RF-11M, sSerial #09/03232985-1, R404A
independent systems.
Cabinet temp 0deg
freezer side suction line freezing up.
suction pressure 18lb. suction line temp ranging from 31deg to -14deg.
8deg DT across the condencer.
Is this large range of suction line temp a sight of a low charge and that's what's causing the suction line to freeze up?
I did do a leak check and found nothing.I used a little PFM to fix it.
-
06-09-2012, 10:53 AM #2
What's the issue here? Not keeping up? Look at the pt chart for 404, at that pressure anything uninsulated is going to freeze? Looks like your superheat is swinging. Bulb insulated?
-
06-09-2012, 10:56 AM #3
-
06-09-2012, 11:00 AM #4
There is no problem cooling the box, just ice on the insulation?
-
06-09-2012, 11:07 AM #5
Better insulate it lol
-
06-09-2012, 11:10 AM #6
-
06-09-2012, 11:12 AM #7
Time for some thicker insulation. I use 1" thick and usually don't have that problem aside from a few seams.
-
06-09-2012, 11:15 AM #8
-
06-09-2012, 11:18 AM #9
Sight glass clear? Temp probe insulated? Single evap or multiple evap system? Are you measuring this at the condenser or inside the freezer?
-
06-09-2012, 11:22 AM #10
-
06-09-2012, 11:55 AM #11
Any driers ahead of the txv? Between sight glass and txv? Suction driers? And yes I'd not be feeling great about the superheat bouncing all over the place like that.