Results 1 to 11 of 11
    May 2008
    Berkshires MA
    freezer/refrigerator
    Servolift, Model RF-11M, sSerial #09/03232985-1, R404A
    independent systems.
    Cabinet temp 0deg
    freezer side suction line freezing up.
    suction pressure 18lb. suction line temp ranging from 31deg to -14deg.
    8deg DT across the condencer.
    Is this large range of suction line temp a sight of a low charge and that's what's causing the suction line to freeze up?
    I did do a leak check and found nothing.
    I used a little PFM to fix it.
    Mar 2009
    Mid-Mo
    What's the issue here? Not keeping up? Look at the pt chart for 404, at that pressure anything uninsulated is going to freeze? Looks like your superheat is swinging. Bulb insulated?
    May 2008
    Berkshires MA
    It's the insulated line thats freezing, The bulb is covered.
    Mar 2009
    Mid-Mo
    There is no problem cooling the box, just ice on the insulation?
    Better insulate it lol
    May 2008
    Berkshires MA
    yup
    Mar 2009
    Mid-Mo
    Time for some thicker insulation. I use 1" thick and usually don't have that problem aside from a few seams.
    May 2008
    Berkshires MA
    so that big suction line temp swing is ok?
    Mar 2009
    Mid-Mo
    Sight glass clear? Temp probe insulated? Single evap or multiple evap system? Are you measuring this at the condenser or inside the freezer?
    May 2008
    Berkshires MA
    sight glass is clear, measure at the low side service, it's a chest style freezer. temp probe is insulated.
    Mar 2009
    Mid-Mo
    Any driers ahead of the txv? Between sight glass and txv? Suction driers? And yes I'd not be feeling great about the superheat bouncing all over the place like that.