    Quote Originally Posted by commtech77 View Post
    Did you do the restoration or did you acquire them in that shape ?
    Are they hard to find parts for ?
    Check my profile theres a bunch of pics there . Yes I did restore the green one and I am now doing the red one . Easy to get parts .
    Aug 2009
    Prattville, Alabama
    Make sure entering and leaving water pressures are determined with one gauge, moved back and forth between the two. And be aware that a restricted, or plugged, evaporator will increase the pressure drop, giving a false indication of flow that is higher than actual. This is where knowing the entering and leaving water temps would be helpful.
    Jun 2012
    whats the formula for gpm. what should the gpm be. Circuit 2 runs for 3min and off on low evap alarm. circuit 1 is running now for the past 2 hrs but when makes temp will be off on same alarm I have 7 psi difference between supply and return,flow switch abviousky is made. suction rftg 58dg sat evap temp 54.7dg,evap psi 92 psi cond psi is 173psi, entering wtr temp 62 and leaving is 58.7 f, thats on circuit 1. Circuit 2 starts and suction drops way down right away and goes off low evap alarm.
    Check the flow with ONE GAUGE!!! Use the search feature!!! How many times do we have to go over this?!?!
    Sound familiar?
    Jun 2012
    I did check with one guage. 7 psi difference.
    ottawa canada
    Heres a novel idea ........................ Call a pro !!!!!!!!!!!!!!!!!!!
    This seems more at home in Tech to tech chat.