    Ground short ?

    Compressor ----
    Copeland
    3 Ph
    560 Volt
    60Hz

    Equipment
    10 ton split custom made (marine)......

    Story.....

    I fly 120 miles in the gulf of Mexico to work on a solenoid valve .... Change it.... All is good....
    I pulled a vac to 700 microns ....
    Dumped recovered gas back in (on both sides) and when I went to start it tripped main breaker. So I took wires off peckerhead and checked to ground. And alas.... Grounded. So.... Does anyone know why? It worked before.... I didn't turn anything on while in vac ....

    "Duct tape is like the force. It has a light side, a dark side, and it holds the world together."

  2. #2
    Join Date
    Jun 2012
    Location
    Queens, New York
    Posts
    66
    Post Likes

    Confused

    Quote Originally Posted by AddMore22 View Post
    Compressor ----
    Copeland
    3 Ph
    560 Volt
    60Hz

    Equipment
    10 ton split custom made (marine)......

    Story.....

    I fly 120 miles in the gulf of Mexico to work on a solenoid valve .... Change it.... All is good....
    I pulled a vac to 700 microns ....
    Dumped recovered gas back in (on both sides) and when I went to start it tripped main breaker. So I took wires off peckerhead and checked to ground. And alas.... Grounded. So.... Does anyone know why? It worked before.... I didn't turn anything on while in vac ....
    When you dumped the recovered gas back in both sides was it liquid?

  3. #3
    Join Date
    Mar 2012
    Location
    Grand Prairie, TX
    Posts
    27
    Post Likes
    I think u charged liquid in suction side. compressor was probably compressing liquid refrigerant.

  4. #4
    Join Date
    Apr 2012
    Location
    Paper Street Soap Company
    Posts
    2,312
    Post Likes
    Topping off the compressor sump with liquid will trash your valves but I doubt it caused an immediate short. Is that for a drive house ?

  5. #5
    Join Date
    Nov 2004
    Location
    up in the hizzy
    Posts
    4,439
    Post Likes
    Quote Originally Posted by commtech77 View Post
    Topping off the compressor sump with liquid will trash your valves but I doubt it caused an immediate short. Is that for a drive house ?

    Besides trashing the valves, the liquid refrigerant washes the oil from the sump, bearings run dry till the rotor collapses shorting the stator to ground. been there,done that.

  6. #6
    Join Date
    Apr 2012
    Location
    Paper Street Soap Company
    Posts
    2,312
    Post Likes
    Quote Originally Posted by valdelocc View Post
    Besides trashing the valves, the liquid refrigerant washes the oil from the sump, bearings run dry till the rotor collapses shorting the stator to ground. been there,done that.
    On a scroll ? I see what you're saying but that specific scenario is limited to semi hermetics.

    You still wash the bearings no doubt but not in a millisecond causing instant short to ground.

  7. #7
    Join Date
    Nov 2004
    Location
    up in the hizzy
    Posts
    4,439
    Post Likes
    Quote Originally Posted by commtech77 View Post
    On a scroll ? I see what you're saying but that specific scenario is limited to semi hermetics.

    You still wash the bearings no doubt but not in a millisecond causing instant short to ground.
    scrolls need oil too, they are more tolerant to flooding cause the pumping mechanism, specially the compliant scrolls.
    There is a misconception about compressors failures due to slugging/flooding, the old "you cant compress liquid" is only a small part of the problem, lack of lubrication is what makes them fail most of the time, it does not happens in a millisecond, depending on the system it may take days or just minutes.

  8. #8
    Join Date
    Apr 2012
    Location
    Paper Street Soap Company
    Posts
    2,312
    Post Likes
    Quote Originally Posted by valdelocc View Post
    scrolls need oil too, they are more tolerant to flooding cause the pumping mechanism, specially the compliant scrolls.
    There is a misconception about compressors failures due to slugging/flooding, the old "you cant compress liquid" is only a small part of the problem, lack of lubrication is what makes them fail most of the time, it does not happens in a millisecond, depending on the system it may take days or just minutes.

    I'm aware of all of that.

    What I meant was the crank on a Carlyse 06E ( FOR EXAMPLE ) obviously runs parallel to the bottom of the unit. So if the bearing in the end bell gets washed out then it allows enough play for physical contact between the rotor and windings.

    So you get get a short to ground.....boom

    The windings and rotor on a scroll are obviously vertical.

    Plus in the last 20 years I've pulled my fair share of heads off of semi-hermetic compressors to see damage from liquid slugging in the form of holes in the top of pistons or broken cranks.

  9. #9
    Join Date
    Apr 2012
    Location
    Paper Street Soap Company
    Posts
    2,312
    Post Likes
    Was the solenoid liquid valve leaking or just inoperable ?

    Did you check it before you replaced the solenoid valve ?

  10. #10
    Join Date
    Mar 2012
    Location
    My house is in Texas..
    Posts
    143
    Post Likes
    Thread Starter
    Quote Originally Posted by commtech77 View Post
    Was the solenoid liquid valve leaking or just inoperable ?

    Did you check it before you replaced the solenoid valve ?
    It was just leaking .....
    It has a receiver.
    Not worried about liquid in suction
    It was in a VFD house.

    "Duct tape is like the force. It has a light side, a dark side, and it holds the world together."

  11. #11
    Join Date
    Aug 2009
    Location
    Prattville, Alabama
    Posts
    4,042
    Post Likes
    What is a "VFD house" ? What kind of device interrupts power to the compressor ? Is it a contactor or something else ? What kind of crancase heater, if any ?

  12. #12
    Join Date
    Mar 2012
    Location
    My house is in Texas..
    Posts
    143
    Post Likes
    Thread Starter
    "VFD" - Variable Frequency Drive- its on a drilling rig.

    It's a 3 phase 600 volt ... So no cap...

    Crank case heater has been disabled prior this.

    I guess my main question is this ...
    Is there any way the insulation in the windings of a compressor be compromised due to a vacuum?

    "Duct tape is like the force. It has a light side, a dark side, and it holds the world together."

  13. #13
    Join Date
    Aug 2009
    Location
    Prattville, Alabama
    Posts
    4,042
    Post Likes
    I thought "VFD" probably meant Variable Frequency Drive, but what exactly is meant by "VFD house" ? EVERYTHING has VFD ? Including compressor ? I realise it has no capacitor, at least I've never heard of a cap used to interrupt power as a means of starting and stopping something, like a compressor... The reason I ask what does start and stop, or interrupt the power to, the compressor is to determine if it is a solid state device ( like a soft starter, or a VFD ). It seems unlikley that it would be anything other that a simple contactor on something this size, but I just wanted to rule it out.

  14. #14
    Join Date
    Apr 2012
    Location
    Paper Street Soap Company
    Posts
    2,312
    Post Likes
    Quote Originally Posted by Nuclrchiller View Post
    I thought "VFD" probably meant Variable Frequency Drive, but what exactly is meant by "VFD house" ? EVERYTHING has VFD ? Including compressor ? I realise it has no capacitor, at least I've never heard of a cap used to interrupt power as a means of starting and stopping something, like a compressor... The reason I ask what does start and stop, or interrupt the power to, the compressor is to determine if it is a solid state device ( like a soft starter, or a VFD ). It seems unlikley that it would be anything other that a simple contactor on something this size, but I just wanted to rule it out.
    Its a seperate building on land and offshore rigs that houses all of the motor control, fuses, controls and VFDs for the DC motors on the rig.

    High heat load and a critical part of any rig. You lose AC and the drives overheat and they have to stop drilling.

    A multi million dollar operation is put on hold until you get the AC repaired.

    Roughnecks and tool pushers looking at you sideways.

  15. #15
    Join Date
    Aug 2009
    Location
    Prattville, Alabama
    Posts
    4,042
    Post Likes
    Quote Originally Posted by commtech77 View Post
    Its a seperate building on land and offshore rigs that houses all of the motor control, fuses, controls and VFDs for the DC motors on the rig.

    High heat load and a critical part of any rig. You lose AC and the drives overheat and they have to stop drilling.

    A multi million dollar operation is put on hold until you get the AC repaired.

    Roughnecks and tool pushers looking at you sideways.
    Ohhh..., OK. Thanks.

  16. #16
    Join Date
    Mar 2012
    Location
    My house is in Texas..
    Posts
    143
    Post Likes
    Thread Starter
    Actually it's a 10 ton with 2 5 ton Copland scrolls. And one legs is always hot with the other two going in a contractor.

    "Duct tape is like the force. It has a light side, a dark side, and it holds the world together."

  17. #17
    Join Date
    Aug 2009
    Location
    Prattville, Alabama
    Posts
    4,042
    Post Likes
    Quote Originally Posted by AddMore22 View Post
    Actually it's a 10 ton with 2 5 ton Copland scrolls. And one legs is always hot with the other two going in a contractor.
    Was unit powered up ( even though not running ) during evacuation ?

  18. #18
    Join Date
    May 2004
    Location
    SE Pennsylvania
    Posts
    2,617
    Post Likes
    Quote Originally Posted by AddMore22 View Post
    And one legs is always hot with the other two going in a contractor.
    There is your problem if you had power to the unit while evacuating. Never pull a compressor under vacuum while windings are powered. Seen it on a job where a co worker suddenly had multiple DOA grounded compressors, went over his install and evac process and he was leaving the unit powered due to 2nd compressor. He hasn't had one since.

    Never mind missed the one post mentioning lock out tag out

  19. #19
    Join Date
    Mar 2012
    Location
    My house is in Texas..
    Posts
    143
    Post Likes
    Thread Starter
    No.... Loto was in place during the evac.
    (lockout tagout)

    "Duct tape is like the force. It has a light side, a dark side, and it holds the world together."

  20. #20
    Join Date
    Aug 2009
    Location
    Prattville, Alabama
    Posts
    4,042
    Post Likes
    Quote Originally Posted by AddMore22 View Post
    No.... Loto was in place during the evac.
    (lockout tagout)
    That's good. And I'm sure you checked it with your meter, right ? Was it running when you got there ? If so, maybe it was just your bad luck to come across a near-failure looking for somebody to dump on.

+ Reply to Thread
Page 1 of 3 123 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •