Results 1 to 13 of 22
    Jun 2012
    Batonrouge
    trane RTU keeps failing
    I have a unit that I cannot find an issue with. Pressures are good, coils are clean but the unit fails over night. Belt was super tight and had black dust on the pully so I changed the belt and check the bearings. Everthing looks good. The tstat keeps reading cool fail when I return but I can never find a problem and the unit runs great all day. Been going on for a few days. Can anyone take a stab at this.
    Southeastern Pa
    Trane stat, or a conventional stat using the interface board?
    Feb 2012
    Toronto Canada
    How cold does it get at Night Below 55? If the temp drops low over night it could be failing cause its not desgined to work in those conditions unless the proper controls where added.
    "Take the batteries out shake them and blow on them. Place them back in and that should do it"
    Jun 2012
    Batonrouge
    It is a trane tstat. And the temp at night is about 85 degrees. During the day temp gets to about 95 or so.
    Southeastern Pa
    Quote Originally Posted by snowbird225 View Post
    Are you saying that the SETPOINT is 85° overnight? What is the overnight ambient temperature?
    Jun 2012
    Batonrouge
    No the set point is 72. The ambient temp is 85 at night and 95 during the day.
    Apr 2006
    Toronto
    the unit fails at night and it starts working in the morning by itself, or do you go out and reset at the disconnect?
    check t-stat programming, change the battery...
    what are the pressures at 95F?
    not much to work with here, more info needed.
    Jun 2012
    Batonrouge
    Yes, I go out in the morning and when I get there it is out on cool fail. So i reset the unit after I look for faults. I was running an 80 psi suction and 255 on the head. (R22) I watched the unit cycle on and off and the tstat seems to be operating great. I pm'ed the other units and kept coming back to check this one and it was running good. suction line sweating and temp in the conditioned space was 72 just as it was calling for it to be.
    Jun 2012
    Batonrouge
    Could the economiser do this
    Mar 2012
    My house is in Texas..
    Is it on any type of control system ?
    "Duct tape is like the force. It has a light side, a dark side, and it holds the world together."
    Jun 2012
    Batonrouge
    No just a trane tstat
    Are there any codes on the UCP board? I had a trane rtu that never gave me any alarms. The whole time the board was showing normal operation, condensor fan motor was the problem. it was tripping on internal overlaod after a few hours of running, also you may want to disable the economizer.
    Apr 2006
    Toronto
    check for power at y1/2 in the morning...if its there than check where control voltage is being held up.
    are there multiple units for this customer or are you on a plaza roof of some kind?