    Can the internal temperature switch be changed on Trane CRHK200 compressor?

    This is a 20 ton compressor on a Trane SFHC AHU. Its the first stage compressor with unloader. It was blowing the control fuse, and I traced the problem to the internal temp switch (schematic shows 2 internal switches). 15 Ohms to ground.

    It looks like the plate where all the terminals are located can be unbolted from the compressor. I am wondering if this is just a Klixon on the back of the plate, or if its somehow wound into the motor.

    I'm hoping to change this small part rather than the whole compressor.

    I'm hoping some of you out there have dealt with this before.
    Thanks for any info!

  2. #2
    Join Date
    Jun 2012
    Location
    Queens, New York
    Posts
    66
    It's more than likely wound into the winding, klixons are surface mount in the terminal Box sensing the shell temperature.

  3. #3
    Join Date
    May 2007
    Location
    NorCal
    Posts
    16
    I was thinking they may be wound in thermistors, but the schematic shows 2 temp switches. I was hoping these were just Kilxons on the back of the plate that can be changed out.

  4. #4
    Join Date
    May 2007
    Location
    NorCal
    Posts
    16
    Wish I could find a cutaway or more info. Thanks for the reply.

  5. #5
    Join Date
    Jun 2012
    Location
    Northern NV
    Posts
    155
    You might try pumping the compressor down and pulling the plate just enough to see if the internal wires are compromised. If it is re-insulating a wire, might be a save. If the switch or thermistor is grounded out in the winding it is a replacement job if you want thermal protection. With switches, you could jump them and run the compressor til it dies should your customer wish this. If it is a thermistor with a control that has some rudimentary smarts that looks for a change in resistance, then it is a change out for sure.

  6. #6
    Join Date
    Oct 2001
    Posts
    6,966
    that one of those big CAN copressors trane put in the rooftop series when thefirst came out.the unloaders are the only thing that can be unbolted off the terminal plate.take them out of the circuit or change the compressor
    "when in doubt...jump it out" http://www.youtube.com/watch?v=U1qEZHhJubY

  7. #7
    Join Date
    May 2007
    Location
    NorCal
    Posts
    16
    This is what I was wondering. Is the klixon mounted to the plate, or to the windings? In other words, if I replace the plate, is the klixon mounted to it, or is the terminal on the plate just for the wires to the internal klixon?

    Thanks for your time,
    Chris

  8. #8
    Join Date
    Apr 2012
    Location
    Paper Street Soap Company
    Posts
    2,304
    Had one do that in a Carlyse O6D. Isolated it and told the compressor we would let it go until it died.

  9. #9
    Join Date
    Aug 2011
    Location
    Pearl Miss
    Posts
    14

    Unhappy

    Can't change them.

  10. #10
    Join Date
    Oct 2001
    Posts
    6,966
    i remember the cover itself had dozen 3/8 screws to view the compressor power wires terminals,unloaders and i swear a HP control and a terminals for an internal thermistor.i was with TRANE service at the time and i think the factory said install a banded temp control to knock the compressor off on over temp,but where to mount it is a mystery 20 yrs later...sorry tell you one thing when those copressor short out it is border line NUKE freon and all items related
    "when in doubt...jump it out" http://www.youtube.com/watch?v=U1qEZHhJubY

  11. #11
    Join Date
    Aug 2006
    Location
    Ohio
    Posts
    2,094
    Quote Originally Posted by commtech77 View Post
    Had one do that in a Carlyse O6D. Isolated it and told the compressor we would let it go until it died.
    Are you the 'compressor wisperer'?

    Do you see dead compressors?


  12. #12
    Join Date
    Oct 2001
    Posts
    6,966
    when TRANE came out with the scrolls in the self contianed they had a discharge temp senser on the top of the compressor.it caused more problems with random trips so they had us cut them out of the circuit...i would cut it out and just run the compressor..if it takes a dump by the time the heat would of built up to trip it the compressor will be cooked.
    "when in doubt...jump it out" http://www.youtube.com/watch?v=U1qEZHhJubY

  13. #13
    Join Date
    Nov 2005
    Posts
    1,350
    Quote Originally Posted by Juan Madera View Post
    You might try pumping the compressor down and pulling the plate just enough to see if the internal wires are compromised. If it is re-insulating a wire, might be a save. If the switch or thermistor is grounded out in the winding it is a replacement job if you want thermal protection. With switches, you could jump them and run the compressor til it dies should your customer wish this. If it is a thermistor with a control that has some rudimentary smarts that looks for a change in resistance, then it is a change out for sure.
    you can put in a resistor with a value that the control will not alarm on. so the compressor is always the right temp if you know what i mean. Until the compressor goes boom. I have had them last for years, and some are still running.
    I STARTED WITH NOTHING, AND I STILL HAVE MOST OF IT!

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event