06-07-2012, 09:22 AM #1
older carrier ahu capacity
Having airflow issues with this unit.
m/n-39ba110a10
s/n-67060694
Chilled and hot water coils. Coils and filters are clean. All dampers are open but church isn't maintaining temp when occupied. Any info on unit would be appreciated. I have our balancer heading out to take readings this week. TIA Fitz
-
06-07-2012, 02:23 PM #2
has it ever worked? were there and changes since? what is the CW temps, the DT across the coils. Is it air flow or temp. To very different things.
you could have flow issues, pumps issues, air etc... did you rule all this out.
-
06-07-2012, 03:44 PM #3
Professional Member*
- Join Date
- Aug 2009
- Location
- Prattville,Alabama
- Posts
- 1,104
Yeah, it sounds as if so far most of the attention has been given to the air side. Don't forget about about the water side.
-
06-07-2012, 10:19 PM #4
Is there air flow (does the fan turn on?). Does the coils get the CHW and HHW?
-
06-09-2012, 10:08 AM #5
Professional Member*
- Join Date
- Feb 2011
- Location
- Chesterfield, Virginia, USA
- Posts
- 84
All "39 Series" Carrier air handlers are purpose built so you will have to call Carrier( and hope you get someone that even knows what they are) to decipher its numbers. It appears to be built in the sixties.
What is the Delta T through the chilled water coils when running? Also how much fresh air are you pulling?
-
06-09-2012, 11:34 AM #6
I'll have more readings for you guys when I return next week. Thanks for the replies. Fitz
-
06-10-2012, 11:21 PM #7
http://www.docs.hvacpartners.com/idc...9b,39c-1xa.pdf
i think this is your unit.