  1. #61
    Join Date
    Mar 2007
    Location
    AR
    Posts
    2,489
    Post Likes
    Thread Starter
    I installed the low temp 404A nozzle that came with the evap

  2. #62
    Join Date
    Mar 2007
    Location
    AR
    Posts
    2,489
    Post Likes
    Thread Starter
    Granted, it could have been the wrong one in the bag i guess. Ive only installed around 12 complete new cooler or freezer systems. This is the first Ive had any problem with. Ill know in the future to verify correct nozzle sizing. How would a bigger nozzle help is what im asking.

  3. #63
    Join Date
    Mar 2007
    Location
    AR
    Posts
    2,489
    Post Likes
    Thread Starter

  4. #64
    Join Date
    Jul 2000
    Location
    Guayaquil, EC
    Posts
    14,652
    Post Likes
    Quote Originally Posted by ar_hvac_man View Post
    Me again Margaret....

    Had a free minute to go check how the freezer is doing. Everything checks out good except my pressure and coil temp. SH 8deg at the bulb. Pressure 15 psi....-20 degree coil. Box hovers at 0 and wont get colder obviously because my suction is too high. My SC is also low at 3 deg but I have a clear sight glass?

    Good SH but I want lower suction so the box will pull down. To get lower suction pressure Id have to squeeze down the TXV which will raise my SH and my evap wont be flooded.

    The distributor nozzle subject keeps scratching at my brain. Can someone explain how going to a bigger nozzle would help?
    The superheat could still stand to be bit lower to around 4-6°F. You'd be amazed at how much difference it can make. But be sure you're measuring the suction pressure at the coil and not at the compressor when you figure the SH because that couple of pounds of pressure drop in the suction line will throw you way off in a hurry at these temperatures.

    Your subcooling usually won't get much higher than what you've got simply because it's got a receiver in the system. There's no adjusting that with charge...or anything else. And yes, by definition at 3°F SC you'll have a clear glass.

    Get it out of your head about altering the suction pressure by messing around with the expansion valve. It's not a pressure regulator...it's a superheat regulator.

    As for the nozzle question, we've already made a fix of sorts by upsizing the TXV capacity. This did one of two things. Either the nozzle was actually OK sizewise and the TXV was undersized...or the other way 'round. So at this point, unless you find you can't get the SH down to where you need it, I wouldn't be concerned about the nozzle sizing. The superheat is a major factor in telling you whether the coil is performing or not.

    The one thing which stands out here is the relatively high TD on the evaporator. You say the box is at 0°F and the coil is at -20°F SST, which gives a 20°F TD. At design conditions it should be a 10°F...but what are the design conditions for this job?

    By the numbers we have, the coil has a specific capacity of 9400 Btuh at a 10°F TD and the condensing unit has a capacity of about 9400 Btuh at -20°F SST and 90°F ambient, so I'm assuming the system was selected for a -10°F box temperature...correct?

    I think a lower superheat will help lower the TD and subsequently raise the suction pressure & lower the box temperature...but another 10°F lower may be a push. Of course there may be other factors in play here.

  5. #65
    Join Date
    Jul 2012
    Location
    Western KY
    Posts
    1,221
    Post Likes
    Quote Originally Posted by crackertech View Post
    Just a thought I once had coil we ordered fore R-22 but it was shipped with a 404 orifice in it drove us crazy.
    That's what I was thinking too. But should see some movement with the adjustment. Wouldn't waste alot of time here. Pull it, verify orifice, and replace valve. Assuming you are confident the charge is correct.

  6. #66
    Join Date
    Dec 2007
    Location
    East Coast
    Posts
    29
    Post Likes
    Would just like to point out the amount of knowledge in this thread. I don't post as often as I should, but read this forum multiple times a week and for any tech that wants to be better this is the place to be. AR...happy you fixed the problem!

  7. #67
    Join Date
    Mar 2007
    Location
    AR
    Posts
    2,489
    Post Likes
    Thread Starter
    Quote Originally Posted by icemeister View Post
    The superheat could still stand to be bit lower to around 4-6°F. You'd be amazed at how much difference it can make. But be sure you're measuring the suction pressure at the coil and not at the compressor when you figure the SH because that couple of pounds of pressure drop in the suction line will throw you way off in a hurry at these temperatures.

    Your subcooling usually won't get much higher than what you've got simply because it's got a receiver in the system. There's no adjusting that with charge...or anything else. And yes, by definition at 3°F SC you'll have a clear glass.

    Get it out of your head about altering the suction pressure by messing around with the expansion valve. It's not a pressure regulator...it's a superheat regulator.

    As for the nozzle question, we've already made a fix of sorts by upsizing the TXV capacity. This did one of two things. Either the nozzle was actually OK sizewise and the TXV was undersized...or the other way 'round. So at this point, unless you find you can't get the SH down to where you need it, I wouldn't be concerned about the nozzle sizing. The superheat is a major factor in telling you whether the coil is performing or not.

    The one thing which stands out here is the relatively high TD on the evaporator. You say the box is at 0°F and the coil is at -20°F SST, which gives a 20°F TD. At design conditions it should be a 10°F...but what are the design conditions for this job?

    By the numbers we have, the coil has a specific capacity of 9400 Btuh at a 10°F TD and the condensing unit has a capacity of about 9400 Btuh at -20°F SST and 90°F ambient, so I'm assuming the system was selected for a -10°F box temperature...correct?

    I think a lower superheat will help lower the TD and subsequently raise the suction pressure & lower the box temperature...but another 10°F lower may be a push. Of course there may be other factors in play here.
    Yes im measuring pressure and temp at the evap. Ill drop the SH a few degrees. I know it is achievable. After the box got down to temp I adjusted the valve and went a little to far so can get it to 4 no problem.

    Good deal on the SC then.

    Yea I know the tev controls SH. With the smaller cartridge pressure was more of where I wanted it at around 8 or 10 psi but as already discussed, I couldnt get SH below 25 at the evap. I did have a colder box though..

    Glad I wont have to unbraze the valve and pull the nozzle.

    The box is in ambient conditions. That was accounted for when they sized it. They set it up for 115 degree ambient and a -15 degree box.

    Ill swing by monday and get the sh to 4 and see how it goes. Just seems like its struggling to maintain 0 and sub 0 temps and is running 24/7, except for three defrost cycles.

  8. #68
    Join Date
    Feb 2008
    Location
    California
    Posts
    2,091
    Post Likes
    Is there a pressure drop between the evap and the compressor?

    I know TXV's are not pressure regulators, But I have seen coils running proper superheat but overloading the suction line and raising the SST. had to increase superheats in order to reduce the load on the suction line to achive desired SST.

    It's rare, but I've seen it

  9. #69
    Join Date
    Mar 2007
    Location
    AR
    Posts
    2,489
    Post Likes
    Thread Starter
    Havnt checked. Will surely take a look monday.

+ Reply to Thread
Page 4 of 4 FirstFirst 1234

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •