Results 1 to 5 of 5
  1. #1
    Join Date
    Oct 2003
    Location
    tidewater, va
    Posts
    2,081
    Hey guys,
    A) Anyone know the torque value for the seal coverplate bolts?
    B)What is acceptable leak rate?
    and C)Do you guys pull these things out with and pre-load them with threaded rod? (that is, are there female threads in the main body to accept say 1/4-20 rod to pull it out evenly like on a York Centrifugal)


    Thanks 404

  2. #2
    Join Date
    Jul 2000
    Location
    Dallas,Texas
    Posts
    4,923
    http://www.xpedio.carrier.com/idc/gr.../5f,h-23si.pdf


    55-60 lbs/ft

    The seal plate will bump off when the bolts are out.
    The seal is a bellows type that is replaced as an assembly.
    You will not need a puller for the seal. Bearing yes.

  3. #3
    Join Date
    Oct 2003
    Location
    tidewater, va
    Posts
    2,081
    wolf,
    thanks for the answer and the link.


    r404a

  4. #4
    Join Date
    Jul 2000
    Location
    Dallas,Texas
    Posts
    4,923
    No problem.

  5. #5
    Join Date
    Jul 2006
    Location
    Cape Cod
    Posts
    157

    5H

    After Seal is installed and some run time you should not have a leak. You will not need a puller but you will have a heck of a time pulling the seal out.