    Confused york yt r123 repairs

    machine shutting down on evap pressure transducer, also ecxessive purge, noticed oil on compressor equalizing line solenoid valve and 3/4 threads below valve. My boss wants me to change these parts on the fly. This machine already has alot of air in it. Should 600lbs of 123 be recovered, also is there a portable purge to remove air since the purge only runs with compressor.

  2. #2
    Join Date
    Mar 2008
    Location
    philadelphia
    Posts
    343
    yes there are portable purges available for purchase to remove the air while it is off line. We have some old purges from Trane chillers that we use. I think you can buy them at redi-controls. How do you know that is the leak and or only leak?

  3. #3
    Join Date
    Apr 2005
    Location
    somewhere out there
    Posts
    87

    york yt

    not sure if it is only leak, it is the only leak I have found. Would it be best to recover 600lbs and leak test with 10 psi of nitrogen, their is another chiller running and this one has had leaks on and off for years. I can not find a way of running the purge on a york without the compressor running like on a trane

  4. #4
    Join Date
    Jun 2012
    Location
    so cal
    Posts
    22
    first of all if you have a yt with a leak issue i would put a redi purge on it so you can get the air out prior to running it. oil purges need the chiller on to work. have you ever heated any machine up to zero and perfomed repairs?

  5. #5
    Join Date
    Jun 2012
    Location
    Los Angeles, California
    Posts
    37

    Do it right the first time

    I would heat up the machine and leak check the entire machine to see where the real leaks are at, as a bare minimum. If the customer will let you pull the gas out even better! That way you can weigh the charge and bump it up with nitro like you said, gas will already be out for what ever leaks you may find. Why is the chiller going off on low evap, may be short. Good reason to weigh the charge. Cover your ass!

  6. #6
    Join Date
    Jun 2012
    Location
    Los Angeles, California
    Posts
    37
    York purges suck, talk customer into letting you replace purge with Trane Purifier. Much more efficeint and like mentioned above can run with chiller off line. Keeps perminent track of purge activity. Sell it.

  7. #7
    Join Date
    May 2011
    Location
    Gateway to the west
    Posts
    21

    York purge

    York purges suck, talk customer into letting you replace purge with Trane Purifier.

    Here's an idea:

    If the purge works correctly, fix the leaks on the chiller
    and leave the purge alone.

    End up saving the customer some money.

  8. #8
    Join Date
    Feb 2010
    Posts
    81
    York purges don't suck, york use gaskets not o'rings or flat face like trane's new gear.

    If your purge is doing work you have a leak.
    I

  9. #9
    Join Date
    Feb 2010
    Posts
    81
    Quote Originally Posted by tacxc View Post
    York purges suck, talk customer into letting you replace purge with Trane Purifier. Much more efficeint and like mentioned above can run with chiller off line. Keeps perminent track of purge activity. Sell it.

    Efficient why, you just rebuild and chiller not tight???