    Trane 5/12 ton ycd, low ambient , 55 space temp

    Hi new to this site, but have some questions about low ambient mechanical cooling, with a space temp of 55 degrees year round, and told to disable economizers.

    2 Trane ycd's .....sorry I do not have the full m#/S#
    1 is 1h/1c 5 ton
    1 is 2h/2c 7.5/10/12 ton?
    ALL CAP TUBES
    #1 stupid idea to disable economizers (Wisconsin)
    #2 if humidity is questionable, use enthalpy controls

    Mods:
    Fan cycling switches
    Lo press switches
    Clixon freez stats
    CCH
    Timers on lps (I recomended delay on break, trane already has delay on make and break, not really necessary) (questionable 30 sec to 2 min depending on what year unit is from)

    Method used to disable economizer: jump out OA sensor
    Problem: resistance above 75 degrees? brings on cond fan #2

    Possible problems:
    Evap icing
    damage to condensate pan/trap/line
    compressor short cycling
    liquid compressor slugging
    oil foaming/blowout
    not air balanced
    condenser coil freezup? Wisconsin?

    Recomendations for low temp applications like this (some not worth it, if mechanical cooling needed, use a Liebert)

    #1 use economizer using adjustable temp controller like the A119 with ucp seeing steady temp, then switched resistance temp to either allow economizer to work or not (this should work, please comment on this!!!!!!!,,,also, does mechanical cooling lock out at 20 degrees? Trane cooling rated at 0 to 115 degrees)
    #2 hot gas & controls
    3 electric evap defrost
    4 electric heaters in return
    5 heat tape for condensate
    6 insulate liquid line
    7 speed up blower fan for lower td
    8 suction accumulators
    9 heated liq line receivers with ORI/ORD valves
    10 txvs

    Trane has a 3 min auto reset lockout after 4 lps trips 1 hr to restart I think.
    Manual reset after 4 hps trips, with 15 min between restart man reset after.
    Changeover from econ to mech after economizer has full open signal, and does not see 0.2 degree/min change...3 min changeover occurs

    Anyone have some helpful input to this?
    Has anyone ever tried this?
    Are the compressors even rated for use at these temps?
    Base of RTU's close to roof line. Any other problems? (Economizer screen freezing/ no oa if econo used, or condenser damage due to ice dam?)

    Thanks guys

  2. #2
    Join Date
    Mar 2004
    Location
    ottawa canada
    Posts
    2,958
    Post Likes
    Your first mistake is to use a unit that is designed to cool/heat a space for comfort cooling ie space temp range 67/85 ish degrees F .
    You need a specialty system designed specifically for your intended use . No amount of modification and fooling around with a rooftop unit is going to provide you with the conditions and reliability you need for the application .
    You need a specialized system period ....
    The toy chest is officially full ... I got a new toy..... 2007 Aston Martin V8 Vantage and yes it still gives me goosebumps
    You bend em" I"ll mend em" !!!!!!!
    I"m not a service tech.. I"m a thermodynamic transfer analyst & strategic system sustainability specialist
    In the new big shop , greasin', oilin' . tweakin' n shinin' !!

  3. #3
    Join Date
    Jun 2012
    Posts
    9
    Post Likes
    Thread Starter
    A lee temp liebert is what would be needed. They can control head pressure well below freezing oa temps, and still be able to maintain 55 degree space temps, and can be ordered, and designed for oa temp/humidity controls for indoor fan, although not too many I have seen bring in oa.

    Has anyone modified a trane rtu for theese types of conditions, without use of economizer?

  4. #4
    Join Date
    Jul 2011
    Location
    East coast USA
    Posts
    1,249
    Post Likes
    Quote Originally Posted by kraftykid View Post
    A lee temp liebert is what would be needed. They can control head pressure well below freezing oa temps, and still be able to maintain 55 degree space temps, and can be ordered, and designed for oa temp/humidity controls for indoor fan, although not too many I have seen bring in oa.

    Has anyone modified a trane rtu for theese types of conditions, without use of economizer?
    what is this going to be used for and what load does it have.

  5. #5
    Join Date
    Jun 2012
    Posts
    9
    Post Likes
    Thread Starter
    Huge sealed insulated chemical drums. Probally highly flamable, and wrecked with moisture I'm guessing.

  6. #6
    Join Date
    Jun 2012
    Posts
    9
    Post Likes
    Thread Starter
    possible plastic aditives? or paint aditives?