Mcquay micrtech II default settings
I have a customer that has a AGZ065 air cooled chiller with the microtech II controller....... they are in an area that is prone to power losses. The machine enable command is defaulted to the off position. I have read the IOM but cannot find directions on changing the default from off to on.
The machine is a stand alone......does not have any external input for enabling the machine.
Thanks
-
06-10-2012, 09:48 PM #2
Professional Member
- Join Date
- Dec 2011
- Posts
- 95
set mode to switches and remove jumper on terminals of start stop,and put switch in place of jumper
-
06-10-2012, 10:04 PM #3
Professional Member
- Join Date
- Dec 2011
- Posts
- 95
mistake,set mode to cool and control mode to switches
-
06-10-2012, 10:13 PM #4
-
06-10-2012, 10:22 PM #5
Professional Member
- Join Date
- Dec 2011
- Posts
- 95
I hope there is a flow switch.And not useing a safty device as a operateing control.
-
06-19-2012, 07:32 PM #6
New Guest
- Join Date
- Jun 2012
- Posts
- 2
New query:
1) I wanted to know why VFD chiller performance curves start sloping downwards below 50 percent load? It follow the power = speed ^ 3 law then why is it sloping downwards after 30 percent load?
-
06-19-2012, 09:19 PM #7
-
06-19-2012, 09:53 PM #8
New Guest
- Join Date
- Jun 2012
- Posts
- 2
Nothing. I am new and I did not know where to post my query. It would be great if someone could answer my question though.