Quote Originally Posted by udarrell View Post
Since beenthere got you on the right track getting more accurate readings, that 22-F temp-split is within a normal range with the humidity percentage level.

Doubt it is running at 1400-CFM... think it running closer to 400-cfm per ton of cooling.

I am back on dial-up (hopefully temporary) & it takes for ever to get a pfd to load. Will look at the pdf later...
You're right - it's set at 1000CFM right now (400cfm per ton). The installer set it at 1400CFM and I switched it back to take the temperature readings.