  1. #14
    Join Date
    Jan 2004
    Location
    PA
    Posts
    69,445
    Post Likes
    The pressure drop means that the pressure at the evap is 37PSIG higher then at the condenser where your taking the reading at.

    I would tap access fittings in at the evap, and see what you really have on both the liquid and suction line.

    What size is the unit.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  2. #15
    Join Date
    Jun 2012
    Posts
    5
    Post Likes
    I wil do that, thanks. its a 5 ton unit.

  3. #16
    Join Date
    Jan 2004
    Location
    PA
    Posts
    69,445
    Post Likes
    A 5 ton should have no real problem working with a 7/8" line. Probably a capacity loss of 3 to 4000 BTUs though.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?