    Confused MIN/MAX read OL on 2 meters

    I have a UEI DL389 and a Fieldpiece HS36 and both these meters will read OL when trying to read inrush/start up amps.

    Are these incapable of this reading?

    I am doing this on resi split systems of 5 tons or less.


    http://www.ueitest.com/sites/default...TA%20SHEET.pdf


    http://www.fieldpiece.com/stick-meters/hs36

    http://www.fieldpiece.com/accessory-heads/ach4
    The Food Stamp Program, administered by the U.S. Department of Agriculture, is proud to be distributing the greatest amount of free meals and stamps EVER.
    Meanwhile, the National Park Service, administered by the U.S. Department of the Interior, asks us to "Please Do Not Feed the Animals". Their stated reason for this policy "... the animals become dependent on handouts and will not learn to take care of themselves."
    from an excerpt by Paul Jacob in Sun City, AZ

  2. #2
    Join Date
    Nov 2009
    Location
    Northwest Illinois
    Posts
    277
    The UEI 389 is not capable of reading inrush. I have the same meter and the same problem. Don't know about the fieldpiece though.

  3. #3
    Join Date
    Jul 2011
    Location
    Stuart, Florida
    Posts
    38
    The HS36 dont have an in rush feature either. Not sure if the UEI has a manual function and set to min max setting, that may work for ya.

  4. #4
    Join Date
    Dec 2007
    Posts
    4,711
    I would have sworn that I was told they both did inrush, but that goes to show what I know and what the counter guys know.

    Thanks

    Fieldpiece SC56 is their only meter to do this, listed as inrush, that I find.
    The Food Stamp Program, administered by the U.S. Department of Agriculture, is proud to be distributing the greatest amount of free meals and stamps EVER.
    Meanwhile, the National Park Service, administered by the U.S. Department of the Interior, asks us to "Please Do Not Feed the Animals". Their stated reason for this policy "... the animals become dependent on handouts and will not learn to take care of themselves."
    from an excerpt by Paul Jacob in Sun City, AZ

  5. #5
    Join Date
    Mar 2007
    Location
    wedged in freezer shelf
    Posts
    6,800
    With the UEi you can change the range and get a better read on a motor like that. Not sure how it compares to the meters with a real inrush feature but you wont OL
    The HS36 Full Auto?
    “If You Can Dodge A Wrench You Can Dodge A Ball”

  6. #6
    Join Date
    Jan 2001
    Posts
    7,862
    With the internet you can read all about something before purchasing. Read the specs, the user manual......everything.....

    Next time do some research before purchasing.

  7. #7
    Join Date
    Jan 2010
    Posts
    66
    Quote Originally Posted by pacnw View Post
    I have a UEI DL389 and a Fieldpiece HS36 and both these meters will read OL when trying to read inrush/start up amps.

    Are these incapable of this reading?

    I am doing this on resi split systems of 5 tons or less.
    I don't own a Fieldpiece, but I know that the UEI will do inrush for you. Here is your issue:

    When you hit the Min/Max button on your UEI, it "locks" you into the range you are in when you hit that button. If you hit the Min/Max button when the display shows 00.00, the max current reading you will be able to capture will be 39.99, because the UEI has a 4000 count display. After that, the screen will show OL for readings over 40A. If you put the range at 000.0 (by using the range button on the unit), now you can read up to 399.9 Amps before you show overload.

  8. #8
    Join Date
    Nov 2009
    Location
    Northwest Illinois
    Posts
    277
    Quote Originally Posted by Fan Blade View Post
    I don't own a Fieldpiece, but I know that the UEI will do inrush for you. Here is your issue:

    When you hit the Min/Max button on your UEI, it "locks" you into the range you are in when you hit that button. If you hit the Min/Max button when the display shows 00.00, the max current reading you will be able to capture will be 39.99, because the UEI has a 4000 count display. After that, the screen will show OL for readings over 40A. If you put the range at 000.0 (by using the range button on the unit), now you can read up to 399.9 Amps before you show overload.
    That's great news! Thanks for the tip!

  9. #9
    Join Date
    Dec 2007
    Posts
    4,711
    Quote Originally Posted by Fan Blade View Post
    I don't own a Fieldpiece, but I know that the UEI will do inrush for you. Here is your issue:

    When you hit the Min/Max button on your UEI, it "locks" you into the range you are in when you hit that button. If you hit the Min/Max button when the display shows 00.00, the max current reading you will be able to capture will be 39.99, because the UEI has a 4000 count display. After that, the screen will show OL for readings over 40A. If you put the range at 000.0 (by using the range button on the unit), now you can read up to 399.9 Amps before you show overload.

    Thanks, I will give that a try.

    I thought that I was shown something like this, but then again maybe not.
    The Food Stamp Program, administered by the U.S. Department of Agriculture, is proud to be distributing the greatest amount of free meals and stamps EVER.
    Meanwhile, the National Park Service, administered by the U.S. Department of the Interior, asks us to "Please Do Not Feed the Animals". Their stated reason for this policy "... the animals become dependent on handouts and will not learn to take care of themselves."
    from an excerpt by Paul Jacob in Sun City, AZ

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event