    Confused do you think i was right and do you consider this a recall

    i recently ran a call at a chain store that we all know. it was for ac no cool in the back room/office. there is two reach in coolers, 1 reach in freezer, 500 lb ice machine also some computers a dishwasher and hot water heater. there are to 5 ton systems at this store. one does only front of the house and 1 is split between the front and back. there are 2 16 in flex returns 1 in the back and one out front. there are 2 12 in supply ducts in the back room and 3 16 in supply ducts out front. originally when i went out i found they had a lightsat that was in holdback because they had books in front of it. for those unfamiliar with these they sense light and when the lights are off they go to unoccupied mode.
    as soon as i removed the books the system came on and had a 20 degree td. went to roof and system was operating properly. i left the call open as i knew i had to come back for maintenance the next day. when i arrived the system was still at 81 degrees but also still running. i closed a supply damper in the front room to push air to the back and preformed regular maintenance.all checked ok. i reccomended that we do a heat load calculation to determine how many cfm of air is need to cool this area.and told them we would be back to do this. today while on another service call i was called and this room was at 96 degrees. another tech ended up out there and he found the condenser fan off due to blown run cap thus the ompressor was cycling on head prerssure. so long story short i got ripped a new one by this tech saying i didnt do it right and there is no problem with ducts. when i was on pm i looked and all looked good cap was not blown at that time and everything was running. just give me your opinion and be honest.i hate getting recalls and this will bother me for weeks. should i have done something diffrent.

  2. #2
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    18,357
    I'd say that stuff happens.
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist

    AOP Forum Rules:







  3. #3
    Join Date
    Jul 2011
    Location
    East coast USA
    Posts
    962
    well happens.

    did you take pressures? SH, SC,? let say you did and everything was fine. Then you have nothing to stress.

    I log everything i do, if i take readings i log it, log OA temp, whatever. so if i get questioned i pull the pad out.... Someday that will happen to the other tech, we all step in burnt compressor oil from time to time.

  4. #4
    Join Date
    Sep 2007
    Location
    State College, PA
    Posts
    1,055
    It is a man made devise that is prone to failure at an undetermined time.

    Maybe the other tech has a crystal ball, I never got mine.
    Can someone please explain to me -
    Why is there never enough time to do it right the first time, but plenty of time to do it twice?


    Please view site rules: http://hvac-talk.com/vbb/showthread.php?t=1241

    Apply for Pro Membership: http://hvac-talk.com/vbb/showthread.php?t=116113

    Find your local HVAC-Talk Contractor: http://icemeister.net/aop_map.html

  5. #5
    Join Date
    Sep 2006
    Location
    Ohio
    Posts
    469
    So did the unit cool the space after he got the condenser fan running? If it did, I would say you didn't spend enough time checking the unit to notice the cond fan not running, or the other tech did more than just replace the capacitor. But everyone misses things from time to time and if we spend too much time on a call, we get our butt chewed.

  6. #6
    Join Date
    Jul 2007
    Location
    Virginia
    Posts
    439
    Well run capacitors being electrical componants just like a light bulb. Its the inrush of current is what usually kills them. You turn on the light one day it works, you turn it on the next day it burns out in a quick flash. Capacitors and motors are really no different, its just a matter of timimg.
    When you do a job, Always make it easier for the next guy, because you may be the next guy working on it.

  7. #7
    Join Date
    Mar 2007
    Location
    N.W.Indiana
    Posts
    59
    I think I would have focused on the Mechanical side of the system not so much on the duct work etc. initially. I don't know if you verified all compressors and condensor motors are were operable, or if your system pressures were good but I would of checked these first.
    We know stuff can happen anytime , but you probably had a condensor motor problem but missed it by not being as thorough as you could of been.
    Start with the mechanical/electrical side and work your way out to the peripherals.

  8. #8
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    4,585
    The other tech ripped you a new one? It's not his place to do that. If he was bustin' your balls, well that's a different story. A callback once in a blue moon isn't going to kill anyone. When it starts happening all the time, you need to reevaluate your diagnostic procedures.
    Officially, Down for the count

    YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET

    I know enough to know, I don't know enough
    Liberalism-Ideas so good they mandate them

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event