    Confused 5 ton trane package unit HP single stage 460v 3 phase.

    evaperator fan turns on amp draw is fine, condenser fan and compressor turn on after delay but only for 5-10 seconds and loses 24 volts to cond. fan relay and to compressor contactor. i have 480 volts at contactor, 24 volts going into control board, high and low pressure switch stay closed, amp draw appears to be fine but not sure dont have much time to check. cond. fan motor and compressor dont feel hot to the touch. i am asuming control board is bad... any help appreciated. thanks guys..

  2. #2
    Join Date
    Oct 2009
    Location
    Raleigh, NC
    Posts
    1,022
    Post Likes
    Does the unit have an economizer?

  3. #3
    Join Date
    Nov 2010
    Location
    cali
    Posts
    96
    Post Likes
    Thread Starter
    Yes but temps were too high and economizer was not open. If econimizer was in use compressor or cond. fan wouldnt even try to start plus economizer would be open.. led indicated for economizer to remain close and run normal single stage cooling.

  4. #4
    Join Date
    Jan 2008
    Location
    Tennessee
    Posts
    62
    Post Likes
    Is this a Voayger unit ? Fault codes would help, but sounds like the High pressure control is tripping. Do you have guages on when it trys to start?

  5. #5
    Join Date
    Jan 2012
    Location
    Orlando, FL
    Posts
    25
    Post Likes
    With the information you gave, sounds like something on the control board is taking out 24V to your contactor shortly after the unit fires up. You mentioned that the Hi/Lo press switches check out fine. Is there anything in your cooling circuit (Y) that could be the culprit? Current sensing relay? compressor lock out relay? Does the control board reset? or is it no longer functioning? If your not finding enough time to check amperage after the unit fires up, "when in doubt, jump it out!" and see whats your amp draw is.
    Last edited by Kon99lbi; 06-01-2012 at 07:32 PM. Reason: added info

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •