    Air in a closed loop system

    Hi, can anyone explain how air gets into a closed loop heating system?

    Thanks

  2. #2
    Join Date
    Aug 2007
    Location
    Northern VA 38 degrees N by 76 degrees W
    Posts
    5,058
    Quote Originally Posted by geochurchi View Post
    Hi, can anyone explain how air gets into a closed loop heating system?

    Thanks
    As in a boiler system?

  3. #3
    Join Date
    Feb 2010
    Location
    In a boiler room
    Posts
    7,049
    If there is a leak somewhere, or the relief valve is intermittently discharging. The fresh make up water brings in oxygen which turns into bubbles.

    Also if you have an automatic air vent in a place that sometimes sees negative gauge pressure. This can happen if system is not piped correctly.

  4. #4
    Join Date
    May 2005
    Location
    Michigan
    Posts
    123

    I agree...

    I've seen auto air vents misapplied on the 3rd floor of a building that were sucking air into the system !

    If your working in a multi-story building, make sure you have about 5 psi at the highest floor...

    Good luck, stay safe,
    I may not be the sharpest knife in the drawer, but compared to some I'm a razor...

  5. #5
    Join Date
    May 2012
    Location
    Upper Michigan
    Posts
    3,588
    Without any other info it's hard to say, but there is no way unless there's a way, air vent, leak, low pressure, relief popped and maybe no water feed.

  6. #6
    Join Date
    May 2004
    Location
    Rapid City, SD
    Posts
    7,414
    Don't forget to check the expansion tank also.

    If you have the old style air over water tank (everything in one tank), sometimes an air vent that's really good can pull the air out of there too from a long ways away in the system.

    If you have a bladder tank, make sure it's still hollow sounding.

    Not a whole lot that can introduce air into a system, but on the other hand, air in the system can sure make you pull your hair out.

    I had a 5 story building I accidentally got some air into. You'd think it would have just settled out in the top floor... but it didn't. Seems like most of the air was in the 3rd floor, and hardly any in 5th.
    "If you call that hard work, a koala’s life would look heroic."

  7. #7
    Join Date
    Aug 2011
    Location
    Salem Oregon
    Posts
    26
    Do you have any Pex pipe in the system? It has to be bought with a specific coating for heating systems. Often it's a red color. The polyethylene itself is oxygen permeable.

  8. #8
    Join Date
    Jul 2010
    Location
    Az
    Posts
    73
    What is the pressure on the inlet side of the pump? Pres reg valve setting (12psi)? if the pump inlet pressure drops below the vapor point the water will vaporize, no air injection needed.
    Attached Images Attached Images  

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event