Scotsman Thermistor Question
Have a scotsman machine (cme656) that has run great up until recently. Both diagnostic lights are on all the time and - according to the restaurant staff - the machine isnt producing properly.
Pulled thermistor plug off board....discharge thermistor in range, water tank thermistor not, reading water temp of 60 degrees when it is in fact 30-32 degrees. Obviously need a new thermistor which was ordered today.
My question is, could failure of the thermistor be causing SUPPOSEDLY lowered ice making capacity?
-
05-31-2012, 06:45 PM #2
Very easy to check production time it and weigh it. 1440 (minutes in a day) / total cycle time (should be around 16 min) = cycles per day x weight of one harvest (should be 6.5-7lbs)
That number should be between 705 and 585
If It's not then maybe something's slowing it down.
I has been my experience that the machine will work with the thermistor bad
Sent from my amazing 4G device
-
05-31-2012, 08:47 PM #3
If the thermistor has failed and both lights are on, it will still produce. Pull the thermistor and put it in a cup of ice water. Then ohm it out while it's in the ice water. This is the actual value from the Scotsman service manual.
32º = 32649 Ohms
If they have to be replaced, i believe the Scotsman part# is 02-3410-21 But don't quote me on that.Every customer you take for granted today will be someone else's tomorrow.
-
05-31-2012, 09:29 PM #4
Professional Member
- Join Date
- Nov 2007
- Location
- NC
- Posts
- 133
Yea, in 32 degree water I'm only registering 15000 ohms. Gotta be replaced.
Again, they called only because they saw the 2 red lights. Then as im there they just kind of mention that it hasnt been producing as much...took it with a grain of salt and ordered the sensor. Just curious if the thermistors have any kind of affect on production since it was kind of a coincidence...
-
06-01-2012, 05:09 PM #5
Professional Member
- Join Date
- Nov 2007
- Location
- NC
- Posts
- 133
Ok. New thermistor cleared my fault codes. For what its worth, in case anybody didn't know this....a clogged condenser coil will cause reduced ice making capacity

Next time ill get my flashlight out of the truck....sigh.....
-
06-01-2012, 05:37 PM #6I love the smell of phosgene first thing in the morning:

To apply for professional membership click here
Educational forums are open.
If you would like to submit a link or an article or other related info to the EF. click here
-
06-01-2012, 07:51 PM #7
-
06-01-2012, 10:03 PM #8
Professional Member
- Join Date
- Jun 2009
- Location
- Garland, TX
- Posts
- 349
Hey, no reason to be upset so long as YOU caught the dirty condenser and cleaned it (of course it would've been better on first trip!) The bad thing is when you've looked at it 3 times, can't figure it out, called tech support, then your service manager comes out and its a dirty condenser...
-
06-03-2012, 05:18 PM #9
Professional Member
- Join Date
- Nov 2007
- Location
- NC
- Posts
- 133
-
06-03-2012, 08:32 PM #10
Professional Member
- Join Date
- Mar 2007
- Location
- Toronto
- Posts
- 258
The Scotsman CME machines have a default freeze mode that bypasses the very finicky thermistor. You turn the machine off, wait 1 minute, then remove the thermistor from the plug on the controller. Hit off again, wait 5 minutes and restart the machine. Both error lights will be on but the machine defaults to condenser fan always on until the pause at the end of the cycle. It will still show other error codes. This seems to work well unless you have a cold room in which case you have to change the thermistor.