Carrier 30gxn.... Anyone seen this?
I have two alarms going off and shutting the chiller down, t999 and t998 both are for "loss of refrigerant flow" one in circuit a and one in circuit b. According to the history it just started happening the other day, the liquid line filters are good ,suction valves are open and I am getting real good flow for the chilled water. Each circuit runs for approx. 3 mins and then they trip off with this alarm. Both EXVs are frosted up after they trip off.
Has anyone seen this before, I find it strange both circuits are acting up at the same time... Telling me it's some thing that affects both ie: chilled water etc
Any help is much appreciated
Thanks
-
05-30-2012, 06:25 PM #2
Although I have never experienced that scenario I would be investigating my liquid line solenoid valves and EXV operation to start. You may have an issue with your EXV driver board.
-
05-30-2012, 06:47 PM #3
Professional Member*
- Join Date
- Jan 2008
- Location
- Dallas ,Texas
- Posts
- 3,509
Yep I'd start ohming out the exv motors. What series is it? How low did your suction pressure go?
UA 100
It takes three people to do anything around here. Two do the work, one explains to the crowd of people who showed up when they seen smoke and flames.
-
05-30-2012, 06:53 PM #4
Regular Guest
- Join Date
- Jul 2006
- Location
- Canada
- Posts
- 59
I am unsure on the series, the suction pressure was dropping right into a vacuum on circuit B and circuit A was running normal pressures for about 3-4 mins then it dropped into a vacuum as well. i will have to ohm out the exv, but when the chiller starts up and goes through its pre start up both EXVs move fully open and fully close
Thanks
-
05-30-2012, 06:57 PM #5
Professional Member*
- Join Date
- Jan 2008
- Location
- Dallas ,Texas
- Posts
- 3,509
-
05-30-2012, 07:04 PM #6
Regular Guest
- Join Date
- Jul 2006
- Location
- Canada
- Posts
- 59
yes
-
05-30-2012, 07:09 PM #7
Professional Member*
- Join Date
- Jan 2008
- Location
- Dallas ,Texas
- Posts
- 3,509
-
05-30-2012, 07:10 PM #8
Regular Guest
- Join Date
- Jul 2006
- Location
- Canada
- Posts
- 59
ok..... that doesn't sound good
-
05-30-2012, 08:34 PM #9
Professional Member*
- Join Date
- Jan 2008
- Location
- Dallas ,Texas
- Posts
- 3,509
UA 100
It takes three people to do anything around here. Two do the work, one explains to the crowd of people who showed up when they seen smoke and flames.
-
05-30-2012, 11:16 PM #10
Professional Member
- Join Date
- Feb 2012
- Location
- utah
- Posts
- 74
why keep it a secret dallas lets have your thoughts. I've seen this many times, low charge, bad exv, bad transducer, loss of program, or in this case I would think since it started happening to both circuits at the same time I would think that the board went bad or the program needs fixn. It seems that with those exv's there was a upgrade in the programing because the number of steps was wrong from the factory.
-
05-31-2012, 07:35 AM #11
Professional Member
- Join Date
- Mar 2008
- Posts
- 103
Dallas Duster
Could I get any info on this fault also? We just started on an account that has had this problem. I am just getting into troubleshooting and thought I would search for any posts about this fault.
Thanks
b-man
-
05-31-2012, 01:48 PM #12
Professional Member*
- Join Date
- Jan 2008
- Location
- Dallas ,Texas
- Posts
- 3,509
UA 100
It takes three people to do anything around here. Two do the work, one explains to the crowd of people who showed up when they seen smoke and flames.