Partially frozen evap, (Thick ice bottom-1/3)
What are some causes for a partially frozen evaporator (besides low charge) on a walk-in evap, 3 fan Larkin food cooler, full charge 404, was running fine, thermostat set on 38, 5 degree differential.
Got a call on this, haven't been there yet. Customer defrosted, but may call me back.
I know that's not much information, but it's pretty much all I have.
I have done all commercial HVAC, not allot of refrigeration, maybe 20%.
Thanks.
-
09-02-2009, 09:42 AM #2
Professional Member
- Join Date
- Jan 2001
- Location
- So.Cal
- Posts
- 425
TXV probably needs to be adjusted, but if you have never done comm refrig you are in for a fun day of tweeking.
-
09-02-2009, 10:47 AM #3
Probably not so much fun,
but thanks for responding.
I will drop by the store and check on it.
-
09-02-2009, 01:23 PM #4
Uneven icing of the evaporator coil like that can be due to an improper distributor nozzle. An oversized nozzle can lead to uneven distribution...essentially overfeed some circuits and underfeeding others.
More than likely though, your ice buildup is a result of incomplete defrosting.
I'm assuming this sytem has no defrost timeclock and relies strictly on the off-cycle time to clear away frost buildup. If ALL of the frost is not cleared off, it will re-freeze and become hard ice.
Add a defrost timeclock and set it up for three 30-40 minute defrosts per day.
-
09-02-2009, 06:54 PM #5
Professional Member
- Join Date
- Jul 2007
- Location
- alexandria va
- Posts
- 138
if its ice not frost make sure your drain is clear. jbb
-
09-02-2009, 08:30 PM #6
X2 check the defrost and the drain line first.
I love the smell of phosgene first thing in the morning:
To apply for professional membership click here
Educational forums are open.
If you would like to submit a link or an article or other related info to the EF. click here
-
09-02-2009, 09:08 PM #7
Professional Member
- Join Date
- May 2004
- Posts
- 1,732
Since this is on the same subject, i have a similar question. What causes the Txv and distributer tubes to freeze to a ball of ice without the coil freezing up? I run into this alot on walk-in freezers.
-
09-02-2009, 09:19 PM #8
Regular Guest
- Join Date
- Jul 2009
- Location
- eastlake,ohio
- Posts
- 73
You're really going to need to know the pressures.High pressure the condenser is dirty or the TXV strainer is dirty,Or you're probably low on refrigerant,Or a evap fan is not working,and of course they might of left the door open all weekend or bad seals.......
-
09-02-2009, 09:37 PM #9
This could happen with a starved TEV. the Liquid is literally flashing to a vapor inside of the TEV.
Or it could be normal and the frost/ice dose not melt in defrost because usually the TEV/distributer tubes are in an enclosed section of the evaporator coil that dose not have heating elements. where as the actual evaporator is in direct contact with the heating elements.
-
09-02-2009, 09:45 PM #10
-
09-02-2009, 10:36 PM #11
-
09-24-2012, 09:50 PM #12
New Guest
- Join Date
- Sep 2012
- Location
- Loma Linda, California
- Posts
- 1
Larkin Walk in cooler freezing up top section only
I started working at a restaurant performing services and the owner asked me to look at their Larkin walk in cooler that was only at 50 degrees. Found large section of inside and outside of coils in walk in frozen up, removed all ice, rooftop unit very low on freon, recharged got temp down to 38 degrees, 3 days later all still ok and coils still clear, 1 week later top section inside and outside frozen up, charge ok but temp down to 50 degrees, is this not defrosting and where could I locate the defroster I cannot find it anywhere. Model # is 2 blade low profile
-
09-25-2012, 03:15 PM #13I love the smell of phosgene first thing in the morning: