New Systems cool as good?
Hi, thanks in advance for your help.
I just had a 22 year old AC unit pulled out and replaced with a new Trane 16i system, with matched air handler and stat. I also have an 8 year old Lennox system as my 2nd unit.
The question I have is the air blowing out of the registers of my 8 year old Lennox system is reading 59 degrees and the air blowing out of the brand new Trane system is reading 69 degrees, full 10 degrees warmer.
Both units are set at 76 degrees on the thermostat, outside temp today is about 100 degrees.
So the question is why? I don't know if the newer R410 refrigerant doesn't cool as well as the older refrigerent or if the new system isn't charged properly. I'm hesitant to sign the completion paperwork until I have a better sense of what is going on.
I was also thinking about replacing the 8 year old unit with a like Trane system, but I'm having 2nd thoughts if there is an issue.
Help!!
-
05-29-2012, 08:54 PM #2
how long has it been running....
it was working.... played with it.... now its broke.... whats the going hourly rate for HVAC repair
-
05-29-2012, 08:56 PM #3
You need to call your contractor back, you have a problem. You may have a charge issue or the system is simply not set up correctly.
Make your expertise uniquely valuable.
Make your influence uniquely far-reaching.
-
05-29-2012, 08:57 PM #4
Regular Guest
- Join Date
- May 2012
- Posts
- 14
Both units have been running all day, the installation was actually completed yesterday
-
05-29-2012, 09:01 PM #5
My guess and its only a guess is the pin switches are not set correctly. I would assume you have a TAM7 air handler and your unit is most likely operating at to high of blower speed.
Make your expertise uniquely valuable.
Make your influence uniquely far-reaching.
-
05-29-2012, 09:03 PM #6
yep don't sign.... not working right yet
it was working.... played with it.... now its broke.... whats the going hourly rate for HVAC repair
-
05-29-2012, 09:07 PM #7
Regular Guest
- Join Date
- May 2012
- Posts
- 14
I didn't get the Tam7 air handler, mine is a 4TEE3F40B1000B.
-
05-29-2012, 09:11 PM #8
-
05-29-2012, 09:14 PM #9
Regular Guest
- Join Date
- May 2012
- Posts
- 14
So does that mean that the air handler is pushing the air out before it has had time to cool?
-
05-29-2012, 09:19 PM #10
the air handler has to be made to match the wanted cfm of the condensing unit... yes hi cfm can cause a low t.d. .... anyway call them back... should be an easy fix....
it was working.... played with it.... now its broke.... whats the going hourly rate for HVAC repair
-
05-29-2012, 09:21 PM #11
Welllllll........ were not cooling it we are removing the heat from it, but basically yes. Your system should be set up to move between 350 to 450cfm per ton depending what part of the country you live in.
Make your expertise uniquely valuable.
Make your influence uniquely far-reaching.
-
05-29-2012, 09:26 PM #12
Your Air handler has a factory setting for 3 1/2 tons, what size is your system?
Make your expertise uniquely valuable.
Make your influence uniquely far-reaching.
-
05-29-2012, 09:34 PM #13
Regular Guest
- Join Date
- May 2012
- Posts
- 14
The 16i condenser is a 3 ton unit


Reply With Quote