Results 1 to 11 of 11
    Dec 2008
    Buffalo NY
    Mr. Slim p8 code
    Hey all, I'm working on a Mr. Slim heat pump and the code p8 is coming up on the stat.
    Model numbers PUH18EK
    PLH18FK
    The unit will run sometimes for ten to fifteen seconds then shutdown. Then it will run for three minutes or so and cool ok then shutdown with the the p8 code. I found some some problems when I opened the condenser. The cap is weak and only putting out 22mfd when it should be 30. Also the voltage going to the unit is 208 and the transformer was hooked up for 230. I corrected the voltage issue but did not get to the cap because it looks special. I did not have much time to play with it but I noticed while it was running the liquid line started freezing up. When I put my gauges on it the pressure on the high side was around 160. I know these things are a different animal from what I usually work on. Looking for some advise on what could be the problem. I will post some pics in a few.
    Join http://scopeny.org/ Shooter’s Committee on Political Education
    The world is full of sheep,try not to join the flock.
    Support the Skilled Trades, Don't DIY
    P8 is an outdoor unit failure code.
    Go to mrslim.com, pull the manual and connect the dots.
    It's the only good way to troubleshoot those wretched things.
    in my lumpy chair
    Before I had any training on them wretched things, I repaired a leak and tried to charge by superheat, sub-cooling, and what the hell is up with the amp draw So I charged it by weight and walked away and confused.
    I dont warranty Tinkeritus
    Dec 2008
    Buffalo NY
    Attachment 265741Attachment 265751Attachment 265761
    In the one pic that molex plug that is corroded was not plugged into anything. I could not find what should be plugged into it. While I was reading the manual it said to ohm the temp sensors that are attached to liquid an suction lines but it does not say what values I should be looking for. It also said it could be the board but I don't want to just throw parts at it. Ugh.
    Sent from my iPhone 4s
    using Tapatalk
    Jan 2006
    Southern MD
    Try this
    http://www.mylinkdrive.com/
    got from tech support a while ago. Has helped me a time or two.
    up in the hizzy
    Quote Originally Posted by qwerty hvac View Post
    using Tapatalk
    The Molex plug is for a second condenser motor, the head pressure is way too low, low and high pressures should be in range with a regular R-22 Ac unit, nothing special about it.
    the thermistors should read between 4.3-9.6Kohms with outdoor temp ranging from 50 to 86F
    Look for a restriction in the liquid line strainer, they are bullet type,hard to spot sometimes, common problem with them units.
    Massachusetts
    Does this help?
    Dec 2008
    Buffalo NY
    Quote Originally Posted by skippedover View Post
    Does this help?
    Thanks for that. I have been reading through one already.
    i believe fault code 8 is for low temperature at evap. coil, i had 2 to do this and found strainer and cap. tube assy. at evap. clogged
    Dec 2008
    Buffalo NY
    Quote Originally Posted by joebear View Post
    Thanks Joe I will check that out when I get time to go back. This just serves one office so it is not a huge rush.
    using Tapatalk
    Dec 2006
    new england
    I had the 8 code a few times. Found the unit low on charge (leak).