No Freeze Stat
Why would a manufacturer depend on the temperature thermistor that cycles the chiller for freeze protection? Yesterday I went out on a MR chiller and found the Glycol running at 2F, everything was iced up. It had locked up the Cold head compressor and one of the LCC Gradient pumps was locked up.
The discharge Glycol/water thermistor went bad and was reading 80F, full speed head at 2F.
Seems like a cheap old Penn control would solve the problem, but its probaly cost $40.
-
05-27-2012, 10:29 PM #2
GE machine? The one with the chinese writing all over it.... Well wait till you see how much that pump is.
It takes courage to grow up and turn out to be who you really are.
- E.E. Cummings
-
05-27-2012, 11:49 PM #3
A better question is why didn't the software program recognize the LWT 78*F higher than the EWT and shut the machine down?
UA LU189
10mm, because it's better than .45acp
-
05-28-2012, 05:56 AM #4
Professional Member
- Join Date
- Feb 2005
- Location
- Florida
- Posts
- 720
-
05-28-2012, 06:02 AM #5
Professional Member
- Join Date
- Feb 2005
- Location
- Florida
- Posts
- 720
-
05-28-2012, 08:50 AM #6
-
05-28-2012, 09:55 AM #7
Professional Member*
- Join Date
- Jul 2007
- Location
- The Hot South
- Posts
- 865
-
05-28-2012, 10:42 AM #8
that is what i am thinking, i would look at a low EWT setpoint,. i would think it should be set up around 35., if this machine has this option,.
if not i would install one., but this machine with factory controls should have some sort of protection.,no signature
blast'em man blast'em
!!!KILL THE TERRORIST!!!
-
05-28-2012, 10:52 AM #9
Professional Member
- Join Date
- Feb 2005
- Location
- Florida
- Posts
- 720
-
05-28-2012, 10:55 AM #10
Professional Member*
- Join Date
- Jul 2007
- Location
- The Hot South
- Posts
- 865
I've seen Trane machines with CH530 controls have leaving chilled water temp sensors fail reading high and the machine would limit on low evap refrigerant temp. Also, they will trip when the leaving temp reads higher than entering temp. The latest software will also cut out on high approach. Kinda triple redundant on freeze protection.
-