    How does water get into my refrigeration system

    Arrived to a call today to find one of the circuits (two scroll compressors) with what looked like water in the sight glasses. This system utilizes a water cooled shell and tube condenser. I have came across water in the refrigeration circuit several times, however I'm trying to find out exactly how this happens. In this case I found this on a maintance and the machine was not running on arrival. The refrigerant is 134A and this skid is used for DX high temperature (comfort cooling). The water pressure from the discharge of the condenser water pump is a constant 40 pound supply. So my question is this, if my refrigerant pressure stays higher then 40 pounds all the time how exactly does water enter into my refrigeration system. I was told that this is due to OSMOSIS. Can somebody tell me if this is true and exactly how this works. I have been looking into this, however mabey somebody can simply explain this to me.

  2. #2
    Join Date
    Dec 2004
    Location
    Chicago area
    Posts
    1,453
    When the bundle fails, the high pressure refrigerant leaks into the waterside until the pressures equalize, then the transfer will go both ways based on temperature difference.

  3. #3
    Join Date
    Nov 2005
    Location
    California
    Posts
    24
    I do not believe this is true because there was more refrigerant pressure when I hooked on to the refrigerant service valves then there was water pressure going through the shell and tube condenser. If your theory was correct then there should have been no water/moisture in the compressors until the pressures equalized. There was 60 pounds of refrigerant pressure at the service valves and only 40 pounds of water pressure at the shell and tube condenser. When I recovered the refrigerant from the sytem I recovered 32 pounds from a factory charge of 36 pounds. Not much refrigerant seemed to dissapear from the sytem. I at first thought like you until it was explained to me by an old instructor that this is the result of osmosis. And that the water pressure does not have to be greater then the refrigerant pressure to get water into your refrigerant.

  4. #4
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    25,957

  5. #5
    Join Date
    Apr 2012
    Location
    Paper Street Soap Company
    Posts
    2,304
    Quote Originally Posted by jpsmith1cm View Post
    Google "Bernoulli's Principle"
    Liquid or gas Pressure and velocity being inversely proportional has what to do with water being in a sight glass ?

    Ive got a A and P license and worked for 3 years on Grumman single engine aircraft so Im a little familliar with that concept. As it pertains to airfoils and caberetors anyway.

  6. #6
    Join Date
    Apr 2012
    Location
    Paper Street Soap Company
    Posts
    2,304
    Quote Originally Posted by excel View Post
    Arrived to a call today to find one of the circuits (two scroll compressors) with what looked like water in the sight glasses. This system utilizes a water cooled shell and tube condenser. I have came across water in the refrigeration circuit several times, however I'm trying to find out exactly how this happens. In this case I found this on a maintance and the machine was not running on arrival. The refrigerant is 134A and this skid is used for DX high temperature (comfort cooling). The water pressure from the discharge of the condenser water pump is a constant 40 pound supply. So my question is this, if my refrigerant pressure stays higher then 40 pounds all the time how exactly does water enter into my refrigeration system. I was told that this is due to OSMOSIS. Can somebody tell me if this is true and exactly how this works. I have been looking into this, however mabey somebody can simply explain this to me.
    Osmosis ? Through copper ? Could be a small amount of moisture left over from some one doing sloppy maintenance.

  7. #7
    Join Date
    Aug 2010
    Posts
    3,727
    Quote Originally Posted by commtech77 View Post
    Liquid or gas Pressure and velocity being inversely proportional has what to do with water being in a sight glass ?

    Ive got a A and P license and worked for 3 years on Grumman single engine aircraft so Im a little familliar with that concept. As it pertains to airfoils and caberetors anyway.

    A good venturi type vacuum pump that runs on compressed air can pull 27" of vacuum.

    If something is getting in through a leak, I would think there's enough air to affect pressure and maybe moisture indicator will show how dry the refrigerant is.

  8. #8
    Join Date
    Apr 2012
    Location
    Paper Street Soap Company
    Posts
    2,304
    Huh ? No. Most techs measure vacuum in microns not inches.

    Its a water cooled condensor and there is water in a sight glass. Hmmmm ?

    Still waiting for a explanation to how Bernoulis principle has amything to do with a busted condensor.

  9. #9
    Join Date
    Jun 2003
    Location
    Chicago, IL
    Posts
    4,568
    Quote Originally Posted by commtech77
    Still waiting for a explanation to how Bernoulis principle has amything to do with a busted condensor.
    If the refrigerant is flowing past the leak area fast enough it's pressure can be lower than the static pressure at the gauge

    I don't think it would be more than 10 psi or so. Also refrigerant doesnt flow fast through a shell and tube condenser so I don't know if it can explain your situation

  10. #10
    Join Date
    Apr 2012
    Location
    Paper Street Soap Company
    Posts
    2,304
    Quote Originally Posted by craig1 View Post
    If the refrigerant is flowing past the leak area fast enough it's pressure can be lower than the static pressure at the gauge

    I don't think it would be more than 10 psi or so. Also refrigerant doesnt flow fast through a shell and tube condenser so I don't know if it can explain your situation
    I think what JP was implyimg was refrigerant flow through the condensor was causing a low pressure condition that dipped well below the 40 psi water pressure.

    That doesnt explain why a shell cooler is leaking. A good vacum would pull water through the heat exchanger.

  11. #11
    Join Date
    Nov 2005
    Location
    California
    Posts
    24
    This is not a small amount on moisture. Water in the the oil sight glass of a scroll 15 ton compressor is not a little water. I removed the main removable shell drier and got water drops coming out of the canister when i was pulling it apart. Both moisture sight glasses were also showing moisture in the system. One sight glass was in the liquid line and the other was in the oil line. This system utilizes a TRAX oil system to help maintain oil level in the two 15 ton parallel scrolls.

  12. #12
    Join Date
    Apr 2012
    Location
    Paper Street Soap Company
    Posts
    2,304
    It doesnt sound good. Sounds like the coolers leaking.

  13. #13
    Join Date
    Feb 2010
    Location
    NE Alabama
    Posts
    301
    If it's leaking it's leaking and the scientific principle behind the leak path isn't the big issue here. If you have found water several times as you stated why isn't as important as where. In a sealed water cooled system as you find on an ac system providing cooling on yachts with a jacketed condenser any water in refrigerant lines is a leak between tubing systems. In larger systems with gasketed heads the leak could be in the gasket or gasket seating surfaces and torque of head bolts would just be one of many reasons for leaking. It's your system and instead of struggling with why find the leak and worry about why later. Scientific principles are just best guesses given with data provided and as such are indicators and not irrefutable answers.

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event