How does water get into my refrigeration system
Arrived to a call today to find one of the circuits (two scroll compressors) with what looked like water in the sight glasses. This system utilizes a water cooled shell and tube condenser. I have came across water in the refrigeration circuit several times, however I'm trying to find out exactly how this happens. In this case I found this on a maintance and the machine was not running on arrival. The refrigerant is 134A and this skid is used for DX high temperature (comfort cooling). The water pressure from the discharge of the condenser water pump is a constant 40 pound supply. So my question is this, if my refrigerant pressure stays higher then 40 pounds all the time how exactly does water enter into my refrigeration system. I was told that this is due to OSMOSIS. Can somebody tell me if this is true and exactly how this works. I have been looking into this, however mabey somebody can simply explain this to me.
-
05-26-2012, 07:17 PM #2
Professional Member*
- Join Date
- Dec 2004
- Location
- Chicago area
- Posts
- 1,386
When the bundle fails, the high pressure refrigerant leaks into the waterside until the pressures equalize, then the transfer will go both ways based on temperature difference.
-
05-26-2012, 08:00 PM #3
Professional Member
- Join Date
- Nov 2005
- Location
- California
- Posts
- 19
I do not believe this is true because there was more refrigerant pressure when I hooked on to the refrigerant service valves then there was water pressure going through the shell and tube condenser. If your theory was correct then there should have been no water/moisture in the compressors until the pressures equalized. There was 60 pounds of refrigerant pressure at the service valves and only 40 pounds of water pressure at the shell and tube condenser. When I recovered the refrigerant from the sytem I recovered 32 pounds from a factory charge of 36 pounds. Not much refrigerant seemed to dissapear from the sytem. I at first thought like you until it was explained to me by an old instructor that this is the result of osmosis. And that the water pressure does not have to be greater then the refrigerant pressure to get water into your refrigerant.
-
05-26-2012, 08:04 PM #4
Google "Bernoulli's Principle"
-
05-26-2012, 08:48 PM #5
Liquid or gas Pressure and velocity being inversely proportional has what to do with water being in a sight glass ?
Ive got a A and P license and worked for 3 years on Grumman single engine aircraft so Im a little familliar with that concept. As it pertains to airfoils and caberetors anyway.
-
05-26-2012, 08:52 PM #6
-
05-26-2012, 08:53 PM #7
-
05-26-2012, 08:59 PM #8
Huh ? No. Most techs measure vacuum in microns not inches.
Its a water cooled condensor and there is water in a sight glass. Hmmmm ?
Still waiting for a explanation to how Bernoulis principle has amything to do with a busted condensor.
-
05-26-2012, 09:08 PM #9
Professional Member
- Join Date
- Jun 2003
- Posts
- 3,642
If the refrigerant is flowing past the leak area fast enough it's pressure can be lower than the static pressure at the gauge
Originally Posted by commtech77
I don't think it would be more than 10 psi or so. Also refrigerant doesnt flow fast through a shell and tube condenser so I don't know if it can explain your situation
-
05-26-2012, 09:26 PM #10
-
05-26-2012, 10:02 PM #11
Professional Member
- Join Date
- Nov 2005
- Location
- California
- Posts
- 19
This is not a small amount on moisture. Water in the the oil sight glass of a scroll 15 ton compressor is not a little water. I removed the main removable shell drier and got water drops coming out of the canister when i was pulling it apart. Both moisture sight glasses were also showing moisture in the system. One sight glass was in the liquid line and the other was in the oil line. This system utilizes a TRAX oil system to help maintain oil level in the two 15 ton parallel scrolls.
-
05-26-2012, 11:46 PM #12
It doesnt sound good. Sounds like the coolers leaking.
-
05-27-2012, 09:29 AM #13
Professional Member*
- Join Date
- Feb 2010
- Location
- NE Alabama
- Posts
- 301
If it's leaking it's leaking and the scientific principle behind the leak path isn't the big issue here. If you have found water several times as you stated why isn't as important as where. In a sealed water cooled system as you find on an ac system providing cooling on yachts with a jacketed condenser any water in refrigerant lines is a leak between tubing systems. In larger systems with gasketed heads the leak could be in the gasket or gasket seating surfaces and torque of head bolts would just be one of many reasons for leaking. It's your system and instead of struggling with why find the leak and worry about why later. Scientific principles are just best guesses given with data provided and as such are indicators and not irrefutable answers.