    Dual circuit over lapping condensers

    Hi,
    I have 2 Trane TTA150B4 condensing units (non heat pump). Each has 2 compressors with two independent refrigerant circuits. The wrap around condensers overlap each other. Both of these units have head pressure problems. I've never been able to get the head pressure down into spec per the manual.

    I have:
    Cleaned the condensers with condenser coil cleaner numerous times.
    Recovered the charges, evacuated and weighed in new charges.

    I spoke with the site engineering supervisor a little while ago about this and he told me that Trane has told him that the only way to clean these condensers is to pull them apart in order to access the area between the single pass coils.
    Pulling apart the dead end of the coil in order to bend it far enough to get between the coils seems like a real bad idea to me. These coils already have a tendency to crack at the header. I've repaired 2 leaks this year alone.
    Has anybody had experience with this type of over lapping condenser coil system. If I can't resolve it I will reccomend replacing both units but I'd like to make sure I've tried everything before I go that far.
    Thank you for your help.

  2. #2
    Join Date
    Jan 2008
    Location
    Dallas ,Texas
    Posts
    3,724
    Yep split the condenser coils the best you can and clean in between the coils.
    UA 100

    It takes three people to do anything around here. Two do the work, one explains to the crowd of people who showed up when they seen smoke and flames.

  3. #3
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    25,777
    1SikLBZ

    This is the Ask Our Pro's forum. In order to post a response here, you must have verified qualifications and have been approved by the AOP Committee. You may ask a question by starting a new thread.

    You can find the rules for posting and qualifications here.

    Additional infractions may result in loss of posting privileges.

    Your post has been deleted.

  4. #4
    Join Date
    Dec 2002
    Location
    in a house, Appomattox, Va.
    Posts
    3,319
    Had one last week w/ high head, normal suction. was overcharged due to pc dirt in piston restricting flow. the sh/sc readings showed where problem was. Thought at first glance was dirty coil.
    Col 3:23


    questions asked, answers received, ignorance abated

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event