Results 1 to 13 of 22
    Nov 2011
    Compressor overheating and shut down???
    system had a leak fixed the leak and charged unit up. At first the compressor turn on and off, Then i opened the main disconnect and restarted it, Compressor turned on and was making a funny noise then stop making the noise, ran for a couple of minutes and then shut off, At the touch of the compressor it was hot. now compressor will not run?????
    History on the unit: hasnet ran in couple of months its a cold room 404A, I barrowed the compressor overload when the unit was unoccupied, to replace a cold room that burnt out its overload, order a new and then installed it back to the compressor wired it the same as the others, charged the system up 22lb of 404A liqiud, and started the unit and now compressor isnt running ????
    Aug 2011
    North West FL
    We are going to need alot more info than that.
    www.mcleanair.com
    "It was working until it quit."
    Oct 2011
    Chicagoland Area
    Soiunds like its broken
    Nov 2011
    Quote Originally Posted by McLean Air View Post
    what kinda of info ?
    Nov 2011
    Had voltage going to the compressor and ohm out the compressor windings seem good.... even when compressor is off the block warms up...
    Aug 2011
    North West FL
    3 phase? Amps? Semi herm? What do your pressures look like when it does run? Why did the old overload fail? What kind of overload? Did you pull a good vac? Did you weigh in a charge? Why 22 pounds of 404? Receiver?
    www.mcleanair.com
    Salt Lake City/Tooele
    Part winding start?
    Apr 2012
    Jackson, MS
    I would Chk my voltage, everything you said leads me in that direction. It could be under, over or you've lost a leg and single phasing. A blown fuse or bad breaker will do this every time. Good luck.
    Jul 2010
    Denver, CO
    Quote Originally Posted by smjrusche View Post
    It sounds like a power problem to me as well. Other things could be a large voltage drop on the contactor or disconnect, loose connection, short to ground, or you didn't wire the new overload correctly (I would recommend wiring it as the manufacturer specifies, not how the other ones are).
    The fact that you can not get it to run now period is a reason for concern. I would recommend being very confident in all your electrical before you attempt to start it again.
    Jan 2012
    WEST COLUMBIA S.C.
    Did u check capacitor
    Nov 2011
    Wired to specs, Contactor chatters a little but its pulled in, got voltage out of the contactor and into the overload and the compressror windings, Compressor trys to start and heats up...
    Nov 2011
    Compressor has been down for a couple of 4 months,
    up in the hizzy
    My guess would be, you liquid charged it too fast washing away the oil and bearings seized up, the funny noise was the liquid refrigerant slugging the compressor, by the time it stopped all the oil was gone.