    Is the vent line solenoid valve the Trane OEM valve and which way does the flow arrow point on it .. To the suction cover or to the oil sump ??
    You bend em" I"ll mend em" !!!!!!!
    I"m not a service tech.. I"m a thermodynamic transfer analyst & strategic system sustainability specialist
    Whooo Hooo spring at last , time to get the toys out ........vrrrroooooom !!!!

  2. #15
    Join Date
    Aug 2000
    Location
    Austell, Ga.
    Posts
    1,246
    Wow.....30 minutes and you lose the entire oil charge. You posted that the compressor was just rebuilt. On that I must ask if the bearing cap and gasket was replaced behind the Ball bearings. Thats the one with the six long threaded studs that go the the rear bearing web. The clearance on that bearing cap to the rotor shaft is extremely close and is often overlooked.
    I did a CVHE1250 and screwed up not replacing it. Strangely it also took 25-30 min to dump all 7 gallons...
    Ain't "None" of us as smart as "All" of us..

  3. #16
    Join Date
    Jan 2012
    Posts
    10
    Arrow points to suction cover and it is oem. Also, i only replaced the gasket. May have been a mistake. It wont lose all 7 gls. in 30 minutes but you can clearly see oil level dropping pretty fast, so i just shut down. But, in the return line sight glass for the thrust bearings you can see a good return to the sump.

  4. #17
    Join Date
    Jan 2012
    Posts
    10
    Update: Problem solved. It was the vent line valve not working. Sounded good but nothing going on inside. Pressurized machine and replaced valve and its running great. Thanks for the tip nuclrchiller

  5. #18
    Join Date
    Aug 2009
    Location
    Prattville,Alabama
    Posts
    1,105
    Quote Originally Posted by djones View Post
    Update: Problem solved. It was the vent line valve not working. Sounded good but nothing going on inside. Pressurized machine and replaced valve and its running great. Thanks for the tip nuclrchiller
    You're welcome, glad it helped.