Gas smell from furnace
I am having this same problem with my Rheem furnace. After it shuts off, there is a gas smell in a certain part of the house. My electronic detector reported combustible gas where I am smelling it, but its sensitivity is greater than what the gas co. uses. The gas co. did not detect the gas.
dbates, did you ever solve your problem? If so, please let us know how you did it - thanks!
-
05-22-2012, 08:47 PM #2
johnnylighton
I started a new thread for you.
-
05-22-2012, 10:01 PM #3
New Guest
- Join Date
- May 2012
- Location
- So Cal
- Posts
- 5
Thanks very much, jpsmith.

To fill everyone on this fine site in with my situation, I have the same phenomenon that dbates had and that one other poster also suffered: there is a smell of gas shortly after my furnace, a Rheem, shuts off.
For me, it's mostly in a certain room and is unmistakeable. I purchased a combustible gas detector for $135 from Amazon that detected combustible gas in the places I smell it in that room, in (what the detector reported) was strong concentrations, after the furnace shut off. It also detected gas coming from 4 of the 5 registers. The strongest gas is near the floor in that room. I could not smell it from the registers with my nose.
But the detector I purchased is not in the same class as professional detectors, and there is no way to set the sensitivity. It's much more sensitive than what the gas co. uses. So I asked the gas co. to come out twice when I smelled (and detected) the gas. Their detector did not register gas, so they told me there was no leak. They also shut the valves to all our gas appliances and pressurized the line, and told me we don't have a leak in the line. I returned the detector because I could not set a base sensitivity.
The dbates thread started included a link to a Honeywell PDF that states there is "trace leakage" of gas after some of their valves shut off, and that a slight smell of gas after the furnace turns off is normal. That document is here: http://hphaa.com/knowledge/FAQs/gas-valve-leakage.pdf
But this is more than a slight problem for us, and I worry about the effects of my family continually breathing this gas.
There is also a small possibility that it's some other type of combustible gas. But that wouldn't explain why the smell is there after the furnace shuts off.
Thank you for any suggestions or solutions!
-
05-22-2012, 10:32 PM #4
1. your nose is a better gas leak detector than any gas detector available.
2. A gas valve is allowed to leak, but I would not tolerate it and replace it.
-
05-22-2012, 11:01 PM #5"Better tell the sandman to stay away, because we're gonna be workin on this one all night."
"Dude, you need more than 2 wires to a condenser to run a 2 stage heatpump."
"Just get it done son."
Dad adjusted
-
05-23-2012, 11:54 AM #6
New Guest
- Join Date
- May 2012
- Location
- So Cal
- Posts
- 5
Thanks for your responses. I forgot to mention: when we bought the house, the sellers purchased a home warranty. I called for service two times and both times the heating contractor said they could not detect a gas leak from the valve or elsewhere. I asked them to send a different service technician for the second call, so we'd have another set of minds thinking about it. The first time they replaced the pilot assembly because that's what the gas co. told me was wrong initially, and the second time they checked the furnace and said it's fine. This home warranty has since expired.
I think the problem is that there is unburnt gas remaining in the furnace, or continuing to flow into the furnace for a short time, after it turns off each cycle. Somehow this is being vented into the house.
-
05-23-2012, 12:00 PM #7
-
05-23-2012, 12:47 PM #8
New Guest
- Join Date
- May 2012
- Location
- So Cal
- Posts
- 5
It's hard to say how old it is. There's a lighting instructions sticker dated 1991 and another dated 1992, so either the furnace itself or the valve only is probably from that time period.
-
05-27-2012, 11:51 AM #9
New Guest
- Join Date
- May 2012
- Location
- So Cal
- Posts
- 5
Problem solved! After spending $$$$ and many hours over the last year trying to figure out where the gas smell in our daughter's room is coming from, I was outside yesterday between our house and the house next door. I smelled gas, and it turns out they have good-sized a gas leak coming out of their crawl space where some gas lines are, which carries over to our house and gets trapped against our house. It then goes into our crawl space through the vents, and up into our daughter's room.
When our heater is on, there is positive pressure in her room. After it turns off, the room is no longer pressurized and more gas can seep in from below. That’s why I associated the gas smell with our heater turning off.
I’m glad I know what’s happening now, but rather ticked that I have gone through the time and money dealing with this when it wasn’t even our problem.
Thank you all for being here and for your kind efforts to help solve this problem.
Last edited by jpsmith1cm; 05-27-2012 at 12:32 PM.
-
05-27-2012, 12:29 PM #10
The gas company should have found that problem. Just walking around outdoors they should have found it.
If YOU want change, YOU have to first change.
If you are waiting for the 'other guy' to change first, just remember, you're the 'other guy's' other guy. To continue to expect real change when you keep acting the same way as always, is folly. Won't happen. Real change will only happen when a majority of the people change the way they vote!