Results 1 to 3 of 3
  1. #1
    Join Date
    Jun 2006
    Location
    SW MO.
    Posts
    5,268
    Post Likes

    This makes no sense.

    Theres no need for a relay on the W circuit. If the wire was broken from the tstat then the relay wouldn't work either. If the W circuit was bad on the board then the relay wouldn't matter. Why ? Why? Why?
    We're awl pawthetic and kweepy and can't get giwrls. That's why we fight wobots.

  2. #2
    Join Date
    Jun 2006
    Location
    SW MO.
    Posts
    5,268
    Post Likes
    Nevermind. Just hit me. They're using the W circuit as a Common to power the Chronotherm tstat. Guess it runs on batteries in heat mode.
    We're awl pawthetic and kweepy and can't get giwrls. That's why we fight wobots.

  3. #3
    Join Date
    Mar 2005
    Location
    burlington county n.j.
    Posts
    9,781
    Post Likes
    isolation relay for a power stealing thermostat.
    protects furnace controls from feedback from thermostat.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.
Comfortech365 Virtual Event