05-26-2012, 07:36 AM #14
Professional Member
- Join Date
- Jan 2011
- Posts
- 676
When values are shown as XXX, it generally means that the values for those points are out of range. If you unplug a transducer you will get XXX for areading. Are you sure the plugs that provide the inputs from the thermistors and transducers are in the correct position and firmly seated on the micro board?
-
05-26-2012, 01:39 PM #15
Regular Guest
- Join Date
- Mar 2012
- Posts
- 7
Ended up we had 2 bad micro processor boards. Replaced with another brd from York today and everything looking good. Thanks for everyone's input