    Trane 800ton only loads to 80%?

    Anyone know what the probable causes to our chiller wanting to only load to 80%? We were told that the "black box" needs to be replaced. I am assuming it is the control box or a device in the control box they are referring to. Just curious Thanks

  2. #2
    Join Date
    Aug 2009
    Location
    Prattville, Alabama
    Posts
    2,020
    Is it controlling to setpoint? Is it controlling "on a limit"? What is the model and serial number (at least first 4 digits of serial no.) of chiller? At least what control panel it has.

  3. #3
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    4,336
    Quote Originally Posted by ZeroTolerance View Post
    ..."black box"...
    i will bet you that this is a clue to the age of the chiller....if so, i think that he may be disappointed.

    (PART-SVB23A-EN)
    "Mother" is the name for God on the lips and hearts of children....The Crow

  4. #4
    Join Date
    Aug 2009
    Location
    Prattville, Alabama
    Posts
    2,020
    Yeah Jay, if that means literally "black" box, you're probably right. I wonder if any of those once available retrofits (based on ch530 parts) are still sitting on any parts shelves anywhere. Just wondering....

  5. #5
    Join Date
    Jul 2007
    Location
    The Hot South
    Posts
    1,310
    What's your current limit set at?

  6. #6
    Join Date
    Dec 2010
    Location
    Central US
    Posts
    414

    Confused

    Ouch!!!!!!!!!!!!!!!!!!! (Black box UCP1) The retrofit kit might be half the cost of a chiller been there and done that last summer.

  7. #7
    Join Date
    Mar 2004
    Location
    ottawa canada
    Posts
    2,043
    Quote Originally Posted by emcontrols View Post
    Ouch!!!!!!!!!!!!!!!!!!! (Black box UCP1) The retrofit kit might be half the cost of a chiller been there and done that last summer.
    Black Boxes are before UCP1
    If its the Black Box Im thinking off then your SOL they are obsolete long time since . Unless you know a very freindly Trane tech who kept one in his garage and has the TOL 90 to set the current calibrator .
    Is it a Classic Black panel with the gauges on the left hand side vertically .
    Time for a controls upgrade and get your wallet out and be ready for a big bill .
    The 64 roars to life Whoo hoo ...shes a rolling chassis .
    You bend em" I"ll mend em" !!!!!!!
    I"m not a service tech.. I"m a thermodynamic transfer analyst & strategic system sustainability specialist
    Best Austin Healey In Show twice in 2013 .....All those hrs paid off .

  8. #8
    Join Date
    May 2010
    Posts
    1,295
    Seriously, this thing is old. It is a base building chiller and the building was built in 1984. The current is set at 100%. It hogs power like a SOB. We are going to eventually replace it in the next year with a new VFD Trane 800ton. Just curious as to what would cause it to only run at 80%

    All I know is that it has four big vertical gauges on the far left front of the black box, about 8 vertical incandescent lights next to the gauges with white levered breakers next to them, and the current and chilled water control is a potentiometer with knobs lol. It is as old as I am.

    Yes healy, I believe you are talking about the one I am.

  9. #9
    Join Date
    Mar 2004
    Location
    ottawa canada
    Posts
    2,043
    Yep thats the one mid 80s Classic Black panel . All obsolete non available parts .
    It could be that the current limit potentiometer is dirty , it could be short of gas , the low evap temp control needs calibrating etc etc .
    You question is way to vague to answer without a full set of accurate readings and even then its a crap shoot .
    you need an experienced Trane tech who is familiar with the older control panels and the black box in the starter to tell you whats wrong with it .
    The 64 roars to life Whoo hoo ...shes a rolling chassis .
    You bend em" I"ll mend em" !!!!!!!
    I"m not a service tech.. I"m a thermodynamic transfer analyst & strategic system sustainability specialist
    Best Austin Healey In Show twice in 2013 .....All those hrs paid off .

  10. #10
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    4,336
    Quote Originally Posted by Healey Nut View Post
    ...If its the Black Box Im thinking...
    that was the one that I was thinking about...V1 and V2!
    "Mother" is the name for God on the lips and hearts of children....The Crow

  11. #11
    Join Date
    Aug 2009
    Location
    Prattville, Alabama
    Posts
    2,020
    I was actually thinking of the solid state overload in the starter for this chiller. I was wondering why I was the only one standing at the starter, while the rest of ya"ll are at the control panel! Not all Trane techs will be familiar with troubleshooting this model. I suspect many newer ones may not be familiar with the special tools required. I know some aren't even aware they exist (the tools, that is).

  12. #12
    Join Date
    May 2010
    Posts
    1,295
    Luckily another one of our buildings has a spare control box they are going to put on for the time being. At least until we get our new Trane VFD 800ton Chiller.

  13. #13
    Join Date
    Aug 2009
    Location
    Prattville, Alabama
    Posts
    2,020
    Exactly what box are we talking about? If it's the one in the starter, there could be a critical adjustment that needs to be made.

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event