Page 1 of 2 12 LastLast
Results 1 to 13 of 26
  1. #1
    Join Date
    May 2010
    Posts
    1,296
    Post Likes

    Trane 800ton only loads to 80%?

    Anyone know what the probable causes to our chiller wanting to only load to 80%? We were told that the "black box" needs to be replaced. I am assuming it is the control box or a device in the control box they are referring to. Just curious Thanks

  2. #2
    Join Date
    Aug 2009
    Location
    Prattville, Alabama
    Posts
    3,171
    Post Likes
    Is it controlling to setpoint? Is it controlling "on a limit"? What is the model and serial number (at least first 4 digits of serial no.) of chiller? At least what control panel it has.

  3. #3
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    6,032
    Post Likes
    Quote Originally Posted by ZeroTolerance View Post
    ..."black box"...
    i will bet you that this is a clue to the age of the chiller....if so, i think that he may be disappointed.

    (PART-SVB23A-EN)
    Don't step on my favorite part of the Constitution just to point out your favorite part.

    Political Correctness is forced on you because you have forgotten decency.

  4. #4
    Join Date
    Aug 2009
    Location
    Prattville, Alabama
    Posts
    3,171
    Post Likes
    Yeah Jay, if that means literally "black" box, you're probably right. I wonder if any of those once available retrofits (based on ch530 parts) are still sitting on any parts shelves anywhere. Just wondering....

  5. #5
    Join Date
    Jul 2007
    Location
    The Hot South
    Posts
    1,859
    Post Likes
    What's your current limit set at?

  6. #6
    Join Date
    Dec 2010
    Location
    Central US
    Posts
    578
    Post Likes

    Confused

    Ouch!!!!!!!!!!!!!!!!!!! (Black box UCP1) The retrofit kit might be half the cost of a chiller been there and done that last summer.

  7. #7
    Join Date
    Mar 2004
    Location
    ottawa canada
    Posts
    2,881
    Post Likes
    Quote Originally Posted by emcontrols View Post
    Ouch!!!!!!!!!!!!!!!!!!! (Black box UCP1) The retrofit kit might be half the cost of a chiller been there and done that last summer.
    Black Boxes are before UCP1
    If its the Black Box Im thinking off then your SOL they are obsolete long time since . Unless you know a very freindly Trane tech who kept one in his garage and has the TOL 90 to set the current calibrator .
    Is it a Classic Black panel with the gauges on the left hand side vertically .
    Time for a controls upgrade and get your wallet out and be ready for a big bill .
    The toy chest is officially full ... I got a new toy..... 2007 Aston Martin V8 Vantage and yes it still gives me goosebumps
    You bend em" I"ll mend em" !!!!!!!
    I"m not a service tech.. I"m a thermodynamic transfer analyst & strategic system sustainability specialist
    In the new big shop , greasin', oilin' . tweakin' n shinin' !!

  8. #8
    Join Date
    May 2010
    Posts
    1,296
    Post Likes
    Thread Starter
    Seriously, this thing is old. It is a base building chiller and the building was built in 1984. The current is set at 100%. It hogs power like a SOB. We are going to eventually replace it in the next year with a new VFD Trane 800ton. Just curious as to what would cause it to only run at 80%

    All I know is that it has four big vertical gauges on the far left front of the black box, about 8 vertical incandescent lights next to the gauges with white levered breakers next to them, and the current and chilled water control is a potentiometer with knobs lol. It is as old as I am.

    Yes healy, I believe you are talking about the one I am.

  9. #9
    Join Date
    Mar 2004
    Location
    ottawa canada
    Posts
    2,881
    Post Likes
    Yep thats the one mid 80s Classic Black panel . All obsolete non available parts .
    It could be that the current limit potentiometer is dirty , it could be short of gas , the low evap temp control needs calibrating etc etc .
    You question is way to vague to answer without a full set of accurate readings and even then its a crap shoot .
    you need an experienced Trane tech who is familiar with the older control panels and the black box in the starter to tell you whats wrong with it .
    The toy chest is officially full ... I got a new toy..... 2007 Aston Martin V8 Vantage and yes it still gives me goosebumps
    You bend em" I"ll mend em" !!!!!!!
    I"m not a service tech.. I"m a thermodynamic transfer analyst & strategic system sustainability specialist
    In the new big shop , greasin', oilin' . tweakin' n shinin' !!

  10. #10
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    6,032
    Post Likes
    Quote Originally Posted by Healey Nut View Post
    ...If its the Black Box Im thinking...
    that was the one that I was thinking about...V1 and V2!
    Don't step on my favorite part of the Constitution just to point out your favorite part.

    Political Correctness is forced on you because you have forgotten decency.

  11. #11
    Join Date
    Aug 2009
    Location
    Prattville, Alabama
    Posts
    3,171
    Post Likes
    I was actually thinking of the solid state overload in the starter for this chiller. I was wondering why I was the only one standing at the starter, while the rest of ya"ll are at the control panel! Not all Trane techs will be familiar with troubleshooting this model. I suspect many newer ones may not be familiar with the special tools required. I know some aren't even aware they exist (the tools, that is).

  12. #12
    Join Date
    May 2010
    Posts
    1,296
    Post Likes
    Thread Starter
    Luckily another one of our buildings has a spare control box they are going to put on for the time being. At least until we get our new Trane VFD 800ton Chiller.

  13. #13
    Join Date
    Aug 2009
    Location
    Prattville, Alabama
    Posts
    3,171
    Post Likes
    Exactly what box are we talking about? If it's the one in the starter, there could be a critical adjustment that needs to be made.

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.