  1. #14
    Join Date
    Jun 2007
    Location
    Jersey
    Posts
    197
    Quote Originally Posted by walterc View Post
    89* isn't that hot. High SC and High SH..
    You might check the other systems and compare.
    It acts like a restriction or bad TXV or even a heavy indoor coil load.
    We declined to work on units in this building. Too much potential liability.
    Any fool can know. The point is to understand. Albert Einstein

  2. #15
    Join Date
    Oct 2009
    Location
    New Jersey
    Posts
    164
    Did you notice that the new building has the condensers outside?

  3. #16
    Join Date
    Nov 2007
    Location
    Sherman, TX
    Posts
    9,441
    Quote Originally Posted by cuervo View Post
    We declined to work on units in this building. Too much potential liability.


    You're joking, right? Liability or incompetence?

    I'm with Walter....find the real problem, instead of looking for excuses....
    Technical incompetence is NOT a sales tool....

  4. #17
    Join Date
    Oct 2010
    Location
    Baton Rouge, LA
    Posts
    1,114
    I am gonna have to side with John on this. Not to be rude but 89°F is nothing for a properly working condenser. If that was my AC not working at 89°, it wouldn't work 8 months of the year.

    High superheat, High Subcooling, High discharge pressure, low suction pressure, yeah sounds like a small restriction or a TXV issues to me.
    If you're too "open" minded, your brains will fall out.
    Artificial intelligence is no match for natural stupidity.

  5. #18
    Join Date
    Apr 2010
    Location
    working overtime
    Posts
    850
    Lol!!!!!!! In my neck of the woods average temp on a roof is 120 degrees . I attended a class from tranr and they said the systems put out these days are not even designed or tested to run in the enviroment down here. That is south west Fl. I agree with the last two posts at 89 degrees that's a walk in the park. Also those are not high efficency units they are gonna run higher head psig. But the condenser needs to be cleaned first chemically. Get out a electric pump sprayer and clean them. Then check the charge if result is still low sucton high superheat and high subcool just replace the valve at that point . Those confitions are no problem. In fact the units should have a charging chart that shows those conditions. My bet is dirty condenser and low on gas. At least you should go through these steps and not just run away.

  6. #19
    Join Date
    Nov 2007
    Location
    Sherman, TX
    Posts
    9,441
    Quote Originally Posted by cavalieri85 View Post
    Lol!!!!!!! In my neck of the woods average temp on a roof is 120 degrees . I attended a class from tranr and they said the systems put out these days are not even designed or tested to run in the enviroment down here. That is south west Fl. I agree with the last two posts at 89 degrees that's a walk in the park. Also those are not high efficency units they are gonna run higher head psig. But the condenser needs to be cleaned first chemically. Get out a electric pump sprayer and clean them. Then check the charge if result is still low sucton high superheat and high subcool just replace the valve at that point . Those confitions are no problem. In fact the units should have a charging chart that shows those conditions. My bet is dirty condenser and low on gas. At least you should go through these steps and not just run away.
    Easier to scream "hack" and run away.....Too many guys think that everything should be installed to lab specifications....and then they get out into the real world.....and discover that we have our own TV channel..."Reality HVAC"......
    Technical incompetence is NOT a sales tool....

  7. #20
    Join Date
    Oct 2004
    Posts
    202
    Would you approve of this?

    To answer your question...

    No... However 89 degrees is nothing.... I would hire a contractor that can properly diagnose and fix the problem....

    Then once the system is fixed... if you want to consider locating the equipment outside of the garage... fine...
    It's all about heat transfer...

  8. #21
    Join Date
    Aug 2011
    Location
    Goose Creek ,SC
    Posts
    252
    Yeah you dont need fire sprinkler water. You can use two pump spray bottles. One to clean and the other to rinse. It is s TXV so you should be focused on subcooling. Sounds like there are bigger issues here than 89 degrees. The 89 degree air is not the problem ,for sure .
    "I just think things should work properly"
    Freon is a brand name-word


  9. #22
    Join Date
    Aug 2011
    Location
    Goose Creek ,SC
    Posts
    252
    Quote Originally Posted by cavalieri85 View Post
    Lol!!!!!!! In my neck of the woods average temp on a roof is 120 degrees . I attended a class from tranr and they said the systems put out these days are not even designed or tested to run in the enviroment down here. That is south west Fl. I agree with the last two posts at 89 degrees that's a walk in the park. Also those are not high efficency units they are gonna run higher head psig. But the condenser needs to be cleaned first chemically. Get out a electric pump sprayer and clean them. Then check the charge if result is still low sucton high superheat and high subcool just replace the valve at that point . Those confitions are no problem. In fact the units should have a charging chart that shows those conditions. My bet is dirty condenser and low on gas. At least you should go through these steps and not just run away.
    And we have a winner
    "I just think things should work properly"
    Freon is a brand name-word


  10. #23
    Join Date
    Mar 2004
    Location
    Chester County PA
    Posts
    422
    ^^with 30* of Subcooling and 22* Delta T? Low charge?^^

    I bet there is a restriction and other people have added refrigerant to keep the indoor coil from freezing up. Completely flooded the condenser and the restriction is acting as a secondary metering device that won't allow the evap to become flooded.

    I'd also lay bet that both coils could use a cleaning.


    Just sayin'

    ~smoke~
    "That motor's done, he let the factory smoke charge out!"

  11. #24
    Join Date
    May 2012
    Location
    Grand Junction, CO
    Posts
    238
    I bet they run better than this one
    Attached Images Attached Images  

  12. #25
    Join Date
    Nov 2007
    Location
    Sherman, TX
    Posts
    9,441
    Quote Originally Posted by GJ-HVAC/R View Post
    I bet they run better than this one
    That would depend on what the deck is made of.....it it's steel grating directly above the unit, it's not a problem....

    In fact, if it WAS steel grating above the unit, you should invite girls in dresses over....tell them that they too, can be like Marilyn Monroe...
    Technical incompetence is NOT a sales tool....

  13. #26
    Join Date
    May 2012
    Location
    Grand Junction, CO
    Posts
    238
    Haha. Good idea. But its decked with 1x6 boards with about 1/8 in gaps

Page 2 of 3 FirstFirst 123 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event