Results 53 to 65 of 74
Thread: Static pressure testing
-
11-30-2012, 12:59 PM #53
Professional Member
- Join Date
- Jan 2007
- Location
- Mn the state where absolutey nothing is allowed
- Posts
- 1,089
answer??? i dont know, thats why im here asking. make no sence to me either. just seams more times than id think i would find blower curves to be off one way or the other.
BT asked if i had a straight supply truck to test, sadly no. so once again today i tested fan only on hi and low, then turned on heat for temp rise method
by tesp/blower curve= hi speed, 1.0"wc tesp ~850-900 cfm as im off the chart.
by 416 traverse in drop = high sp= 1038 cfm
by temp rise method = 1042 cfm
on low speed, tesp/ bc = 0.71"wc and 515 cfm
by 416 traverse in drop = 849 cfm
by temp rise method = 912.
my head hurts, if didnt have to go to work in an hour, id have a beer.
ps yes energy star i understand that NCI inst recognised. i have no horse in that race, im looking to learn diagostic for residention existing systems 'cause that where i live.
but pls if you have some insight that will help my understanding i am all ears. thank you.......my boss thinks its possible to repeal the laws of physics
-
11-30-2012, 01:08 PM #54
It is more than likely that what BT said about not having a straight piece of duct to test. Based on everything I've read (although there is always disagreement) using a ductblaster as a active (powered) flow hood is the more accurate method for testing air flow in residential systems. The following study indicates they a vastly more accurate than other flow hoods. http://epb.lbl.gov/publications/pdf/lbnl-49697.pdf
An answer without a question is meaningless.
Information without understanding is useless.
You can lead a horse to water............
http://www.mohomeenergyaudits.com
-
11-30-2012, 01:18 PM #55
Professional Member
- Join Date
- Jan 2007
- Location
- Mn the state where absolutey nothing is allowed
- Posts
- 1,089
can i borrow your ductblaster?
yeah ive read about those too.
oh well, this is only one system. ive decided to forget about for a while. but am still looking for example from other techs and ideas/info from the TAB guys.
peace outmy boss thinks its possible to repeal the laws of physics
-
12-04-2012, 03:25 PM #56
-
12-04-2012, 04:07 PM #57
Why would it matter if NCI is recognized by AABC? They are another balancing organization.
There are a lot of architects and engineers accepting NCI certification on their projects. On some projects it is actually being spec'd.
If they accept a submittal package for the NCI certification, then NCI certification is absolutely valid for that architect or engineer.Have you set up a Google alert for Carbon Monoxide yet?
Click here to find out how.
-
12-04-2012, 04:10 PM #58Have you set up a Google alert for Carbon Monoxide yet?
Click here to find out how.
-
12-04-2012, 04:18 PM #59
-
12-04-2012, 04:28 PM #60
-
12-04-2012, 04:30 PM #61
davidr
It is not the same.Always here
-
12-05-2012, 12:43 PM #62
see this is where the problem with manufacture data..no standards. I have learned to take esp readings from after the filter and before the a/c coil. and was confirmed here....yet I download my service manual and it shows this:
aaaand I'm confused again......
Sent from my BlackBerry Runtime for Android Apps using Tapatalk 2
-
12-05-2012, 03:34 PM #63
My G50UH service manual says this in the notes of blower performance data: Also see Filter Air Resistance table.
Which means if you place the probe before the filter as they show in your picture, you still need to account for the PD of the filter based on the Filter Air Resistance chart in the manual.
Either way works.Instead of learning the tricks of the trade, learn the trade.
-
12-05-2012, 05:21 PM #64
-
12-05-2012, 07:44 PM #65
You should always take static pressure readings when you suspect airflow problems. Signs of airflow problems could be furnace tripping on high limit, low suction pressures, icing evaporator. Most furnaces will have the design Total External Static Pressure (TESP) listed on the nameplate. If your total TESP is more than what the manufacture specifies, your duct work it too restrictive and the fan will not deliver the designed airflow. Your TESP measurement should include filter pressure drop. Measure the discharge static in the supply plenum far enough downstream to minimize turbulence. Measure the return static downstream of the filter and before the fan.
TESP will not tell you how many CFMs the fan is delivering only that the duct resistance it too high to deliver the design CFM. Most situations you might find that the return is too restrictive. There are many causes of too much restriction in the duct but thats another discussion. You might also find that the pressure is too low. Too low of a TESP can cause problems with some equipment. Mainly, to low of a pressure can cause fans to over amp and with some units can cause fans not to perform.



Reply With Quote