    It is not the same.
    Always here

  2. #62
    Join Date
    Jan 2011
    Location
    Ottawa, Canada
    Posts
    470
    Post Likes
    Quote Originally Posted by beenthere View Post
    Between filter and furnace.
    see this is where the problem with manufacture data..no standards. I have learned to take esp readings from after the filter and before the a/c coil. and was confirmed here....yet I download my service manual and it shows this:

    Name:  uploadfromtaptalk1354729374075.jpg
Views: 545
Size:  57.7 KB

    aaaand I'm confused again......

    Sent from my BlackBerry Runtime for Android Apps using Tapatalk 2

  3. #63
    Join Date
    Jul 2007
    Location
    Virginia
    Posts
    19,250
    Post Likes
    Quote Originally Posted by DeHeatify View Post
    see this is where the problem with manufacture data..no standards. I have learned to take esp readings from after the filter and before the a/c coil. and was confirmed here....yet I download my service manual and it shows this:
    aaaand I'm confused again......
    My G50UH service manual says this in the notes of blower performance data: Also see Filter Air Resistance table.

    Which means if you place the probe before the filter as they show in your picture, you still need to account for the PD of the filter based on the Filter Air Resistance chart in the manual.

    Either way works.
    Instead of learning the tricks of the trade, learn the trade.

  4. #64
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Quote Originally Posted by DeHeatify View Post
    see this is where the problem with manufacture data..no standards. I have learned to take esp readings from after the filter and before the a/c coil. and was confirmed here....yet I download my service manual and it shows this:

    Name:  uploadfromtaptalk1354729374075.jpg
Views: 545
Size:  57.7 KB

    aaaand I'm confused again......

    Sent from my BlackBerry Runtime for Android Apps using Tapatalk 2
    Yeah, standardization would be nice.

  5. #65
    Join Date
    Jun 2004
    Location
    Eugene, Oregon
    Posts
    1,015
    Post Likes
    You should always take static pressure readings when you suspect airflow problems. Signs of airflow problems could be furnace tripping on high limit, low suction pressures, icing evaporator. Most furnaces will have the design Total External Static Pressure (TESP) listed on the nameplate. If your total TESP is more than what the manufacture specifies, your duct work it too restrictive and the fan will not deliver the designed airflow. Your TESP measurement should include filter pressure drop. Measure the discharge static in the supply plenum far enough downstream to minimize turbulence. Measure the return static downstream of the filter and before the fan.
    TESP will not tell you how many CFMs the fan is delivering only that the duct resistance it too high to deliver the design CFM. Most situations you might find that the return is too restrictive. There are many causes of too much restriction in the duct but thats another discussion. You might also find that the pressure is too low. Too low of a TESP can cause problems with some equipment. Mainly, to low of a pressure can cause fans to over amp and with some units can cause fans not to perform.

  6. #66
    Join Date
    Oct 2010
    Location
    Anderson, South Carolina, United States
    Posts
    21,021
    Post Likes
    Went on a call about a month ago, gas pack had been through 3 ECM blower motors in 7 years they called us bc the company that changed the motors said they will only warranty the same piece 3 times in the 10 year warranty period, went out and opened the blower compartment door and the 18" flex was completely disconected from unit. How the other tech didn't see this when changing the blower 3 times is beyond me. Fixed the duct and put new motor in and the next day the customer called and asked what we did bc the unit was keeping the house cool and not running all the time like it had. There was not sp on the return duct causing the motor to overamp and burn up the ECM motor. Had it been a psc it would have pulled less amps.

  7. #67
    Join Date
    Jul 2008
    Location
    Rochester NY
    Posts
    5,298
    Post Likes
    Quote Originally Posted by DeHeatify View Post
    So if it's included am I to be taking the measurement from upstream or downstream of the filter? I have wondered this before...

    Sent from my SGH-I747M using Tapatalk 2

    Quote Originally Posted by ch4man View Post
    can i borrow your ductblaster?

    yeah ive read about those too.
    :-)

    Quote Originally Posted by DeHeatify View Post
    So if my manual says this. Do I take the measurements before or after the filter?

    Attachment 333041
    You might want both. Nice to know sp of filter, just like nice to know coil.

    So, drilling into the fan compartment, ok. But if coil directly atop furnace, what? Definitely not comfortable drilling coil box. There some trick to this?

  8. #68
    Join Date
    Jan 2011
    Location
    Ottawa, Canada
    Posts
    470
    Post Likes
    Quote Originally Posted by tedkidd View Post
    :-)

    So, drilling into the fan compartment, ok. But if coil directly atop furnace, what? Definitely not comfortable drilling coil box. There some trick to this?
    I've drilled right at the edge where the plenum meets the furnace casing.

    Sent from my GSIII on Tapatalk

  9. #69
    Join Date
    Jan 2007
    Location
    Mn the state where absolutey nothing is allowed
    Posts
    2,516
    Post Likes
    Quote Originally Posted by tedkidd View Post
    :-)



    You might want both. Nice to know sp of filter, just like nice to know coil.


















    So, drilling into the fan compartment, ok. But if coil directly atop furnace, what? Definitely not comfortable drilling coil box. There some trick to this?
    i drill a boat load of holes when testing. i use a 3/6" - 1/2" step bit. as for as the hole above standard furnace and below a-coil. keep an eye on the drain port. there should be no part of the coil below that.

    some times even that isnt enough, such as cases coils. then the back of the furnace cabinet gets stabbed. if everywhere seems impossible a final option woulg be to replace any screw in the faceplate with a #10 panel screw and use the 1/8" diameter 12" pitot tube that dwyer sells. 1/8" tubing fits in a hole left by a # 10 screw
    my boss thinks its possible to repeal the laws of physics

  10. #70
    Join Date
    Jul 2008
    Location
    Rochester NY
    Posts
    5,298
    Post Likes
    Quote Originally Posted by ch4man View Post
    i drill a boat load of holes when testing. i use a 3/6" - 1/2" step bit. as for as the hole above standard furnace and below a-coil. keep an eye on the drain port. there should be no part of the coil below that.

    some times even that isnt enough, such as cases coils. then the back of the furnace cabinet gets stabbed. if everywhere seems impossible a final option woulg be to replace any screw in the faceplate with a #10 panel screw and use the 1/8" diameter 12" pitot tube that dwyer sells. 1/8" tubing fits in a hole left by a # 10 screw
    Awesome, Thanks!!!

    ... on the bit, I know I need to get one of those. Just keep flaking it.

  11. #71
    Join Date
    May 2007
    Location
    Central NJ Area
    Posts
    1,248
    Post Likes
    I remove the limit, apply a piece of foil tape over the opening, and take my reading there if there isn't any room between the coil and the furnace.

    Teddkid, I don't know how you deal with the weather in Rochester. I went to RIT back in 1999-2001. The lake effect snow and wind up there is killer. I realized why they had tunnels underground on campus to get around!

  12. #72
    Join Date
    Oct 2010
    Location
    Anderson, South Carolina, United States
    Posts
    21,021
    Post Likes
    Quote Originally Posted by tedkidd View Post
    :-)



    You might want both. Nice to know sp of filter, just like nice to know coil.

    So, drilling into the fan compartment, ok. But if coil directly atop furnace, what? Definitely not comfortable drilling coil box. There some trick to this?
    I cut a piece of 3/8 copper tubing and sleeve the bit only allowing the tip to make the hole, the copper stops the bit from penetrating any further and do any damage.

  13. #73
    Join Date
    Dec 2012
    Posts
    1
    Post Likes
    Hi I heard about static pressures in class, but was never utilized. I feel like i am missing something huge. Is there a manual for newbees on static pressure measuring, where to measure, and what kinds of measurments we are supposed to see for different issues like blocked return etc....? Great topic

  14. #74
    Join Date
    Jul 2007
    Location
    Virginia
    Posts
    19,250
    Post Likes
    Quote Originally Posted by amana_heatingandair View Post
    Hi I heard about static pressures in class, but was never utilized. I feel like i am missing something huge. Is there a manual for newbees on static pressure measuring, where to measure, and what kinds of measurments we are supposed to see for different issues like blocked return etc....? Great topic
    Welcome to HVAC-TALK. If you have scanned a few of the other posts in this "OPEN" (anyone can view) Tech-Tech forum, you probably have noticed we don't post manuals or technical information. This Tech-Tech forum is just a means for guys like you to work on getting Pro membership without getting too technical.

    If you get your post count up to 15, and apply for PRO membership, it will allow you into the "LOCKED" Pro side of this forum where we openly talk and post technical information.

    The other very important thing to do, is fill out your profile on this forum (under Forum Actions), including an email address (Stomp! Stomp!), so we can read a little about you.

    So to answer your question, there is a lot of info/references on this subject that we would love to pass onto you, but can't until you get pro membership.

    Again welcome, and look forward to seeing you on the other side.
    Instead of learning the tricks of the trade, learn the trade.

+ Reply to Thread
Page 4 of 4 FirstFirst 1234

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •