Results 27 to 39 of 74
Thread: Static pressure testing
-
11-26-2012, 10:37 PM #27
-
11-27-2012, 05:05 AM #28
-
11-27-2012, 05:52 AM #29
I always check esp. Based on blower performance, I know what the unit is moving and use this as a starting point. I don't see how you can charge a system without it.
-
11-27-2012, 04:32 PM #30
It is good to see someone mention system effect. The way so many residential duct systems are designed... I would love to see a field study of actual measured air flow of a large amount of systems to see how far off most of them are as compared to their blower performance charts.
An answer without a question is meaningless.
Information without understanding is useless.
You can lead a horse to water............
http://www.mohomeenergyaudits.com
-
11-28-2012, 06:21 AM #31
We design our systems to deliver 350 cfm's at .5 esp. After setting the blower speed and verifying our static, we do the air balance. As it turns out, we do deliver what we designed better than 95% of the time. This includes multi system houses, damper systems, upflows, horizontals, and any combination of.
The company I work for does 80% of RNC in our area. Good enough for a field test?
I don't want to come across as being a know-it-all but anyone who says static pressures don't matter is wrong. Air flow is probably more important than mechanics in our industry. It's also the most difficult to understand.
If your static pressures aren't right, than nothing else about your system will be right.
-
11-28-2012, 07:42 AM #32
The qualm I have with blower charts is that liitle subnote....."air filter included ". Ok well without publishing the Pd it leaves it to interpretation.
-
11-28-2012, 08:37 AM #33
-
11-28-2012, 08:47 AM #34
This is what I mean .... a lot is left to interpretation.
From the manufactures standpoint they say to take reading upstream. But without publishing the Pd across that factory included filter it is hit or miss IMO.
With that said they are usually talking about a very loose weaved fiberglass. And a Pd of .1 - .2 at the most.
Carrier does do a good job of publishing their data for those metal framed blues but those let a lot of dirt through also.
-
11-28-2012, 04:40 PM #35
-
11-28-2012, 04:49 PM #36
Professional Member*
- Join Date
- Apr 2009
- Location
- Texas
- Posts
- 218
The number one thing that checking static pressure has helped me with is fixing condensation problems. Almost all the horizontal attic units that I've seen with a pan full of water under them have shown to be off on static pressure. Some have a hole in the primary pan of course, but on the ones that didn't have a hole and that I've taken whatever measures to get the static right on, have dried up and not had condensate leaks again.
-
11-29-2012, 08:26 AM #37
Professional Member
- Join Date
- Jan 2007
- Location
- Mn the state where absolutey nothing is allowed
- Posts
- 1,097
i took NCIs air diagnostic and balance class last year and this past summer was living and breathing capacity checks.
it seemed to me that blower curve are more of a guideling than actual numbers. too much imterpolation ( although what does that say to a TAB guy who uses fan laws regularly?). way more times than i ever expected the capacity checks reveiled something amiss with my calculations and always pointed to the CFM number i plugged into the total and sensbile formulas,
my own furnace is a mid eff amana with a 3 ton blower package. horrible ductwork with the most restriction on the return ( yeah i know, and doctors make the worst patients).
the following numbers are approx as i didnt record them but close enough to make my point,
the factor blower curve claims on low speed tap at 0.88" tesp to deliver approx 650 CFM. ok sounds about right?. well a return drop traverse with a testo 416 claimed 1100 CFM ,, huh! a 3 ton blower on low at 0.88 tesp. cant be.
but the capacity check showed terrible cooling numbers with no dehumidifcation. and this was just after i did a clean and check of my AC. SH &SC numbers right on. if i use 650 CFM in the total heat formula made no sense, yet if i plugged in 1100 CFM my capacity check results fell into place..
this is only one example. most times wile doing rebate data collection cap checks show way less airflow than ecm dipswitchs lead you to believe..
Tips, you sound like a TAB guy, any thoughts?
you are correct, airflow is the most important check to do. but static presure doesnt alway mean airflowmy boss thinks its possible to repeal the laws of physics
-
11-29-2012, 08:38 AM #38
-
11-29-2012, 10:27 AM #39Not officially trained in it. I'm a bit of a AUTODIDACTIC POLYMATH. I have tried to get people talking about system effect whenever I've seen threads regarding air flow & how to check it, but havn't had much luck. You being trained in TAB maybe will be better able to help get this knowledge out more than it is. Thanks for sharing your story about your own system. I hope that gets peoples attention.Tips, you sound like a TAB guy, any thoughts?An answer without a question is meaningless.
Information without understanding is useless.
You can lead a horse to water............
http://www.mohomeenergyaudits.com



Reply With Quote