carrier package unit
i work on alot of carrier package units, thanks to walgreens. roughly 10 tons 2 stage cooling , 2 seperate circuits. anyways i seen there is a pressure switch on the discharge line and one on the liquid line! its NOT a heat pump, they are all like this so i assumed one on liq. line was a fan cycling switch until i said let me trace the wiring. pressure setting is faded off anyways they are in series together tied to the famous carrier lockout board. Why 2? i called tech support the guy told me the one on the discharge line is hi press. cutout. the one on the liquid line is a loss of charge (similiar to a low press switch). he said they do that on all the heat pumps so in the heat mode it will sense low pressure. ok cool but this is not a heat pump then he told me no even on the straight cool units they still put it there from factory so there is no confusing on the location. he said in this situation it serves no purpose and basically i have no low pressure protection. i think that is really stupid who do they have installing them??????????
-
05-19-2012, 07:42 PM #2[Avatar photo from a Florida training accident. Everyone walked away.]
2 Tim 3:16-17
RSES Certificate Member
AOP Forum Rules:
-
05-19-2012, 07:46 PM #3
Professional Member
- Join Date
- Sep 2010
- Location
- miami,fl.
- Posts
- 317
if its almost completely out of gas then i can see it serving its purpose, and it will probably cut out. but i agree just install one.
-
05-19-2012, 09:15 PM #4
Professional Member*
- Join Date
- Jan 2008
- Location
- Dallas ,Texas
- Posts
- 3,506
It all work correctly as designed. In theory where are the possibilities of a freeze up, right past the drier . The drier protects the metering devices. The switch has a cutout of 7 psi. The mist safety in this sequence is the freeze stat on the evaporator coils. That is basically your main low pressure protection.
UA 100
It takes three people to do anything around here. Two do the work, one explains to the crowd of people who showed up when they seen smoke and flames.
-
05-19-2012, 09:41 PM #5
In theory....
When I see a 7 psi switch on a liquid line, I have to ask myself: how long will that compressor be able to run at 8 psi before the compressor takes its last breath? At 8 psi on the liquid line, what is the low side pressure? Oil return?
I'm going with a low pressure switch.[Avatar photo from a Florida training accident. Everyone walked away.]
2 Tim 3:16-17
RSES Certificate Member
AOP Forum Rules:
-
05-19-2012, 10:03 PM #6
Professional Member
- Join Date
- Sep 2010
- Location
- miami,fl.
- Posts
- 317
if your txv bulb gets stuck closed the evap wont freeze due to no refrigerant passing through, also the location on the freeze stat is about 3/4 up from the bottom of the evap coil. lack of ref. will not freeze all the way up, at times it might not trip. but there are many different scenarios we can go with, but my main point was that the guy from tech support said its just there so at the factory they dont get confused. and it is useless on this application.
-
05-19-2012, 10:09 PM #7
Professional Member*
- Join Date
- Jan 2008
- Location
- Dallas ,Texas
- Posts
- 3,506
-
05-19-2012, 10:10 PM #8
Professional Member*
- Join Date
- Jan 2008
- Location
- Dallas ,Texas
- Posts
- 3,506
-
05-19-2012, 10:19 PM #9
Professional Member
- Join Date
- Sep 2010
- Location
- miami,fl.
- Posts
- 317
-
05-19-2012, 10:22 PM #10
Professional Member*
- Join Date
- Jan 2008
- Location
- Dallas ,Texas
- Posts
- 3,506


Reply With Quote