Thread: OIL SEPARATORS
-
05-07-2012, 09:34 PM #1
Professional Member
- Join Date
- Jan 2010
- Posts
- 4,410
OIL SEPARATORS
there on a 10 ton split system for A/C. Originally it was a water cooled air handler. Someone added a air condenser on the roof. Two 5 ton Copeland CRN-5's on separate circuits. Hot gas goes into separators then up to roof. The one dead compressors separator looks like a major leakier. I would like to cut it out and bypass it. Yes, No, or Maybe ?
-
05-08-2012, 09:04 AM #2
Regular Guest
- Join Date
- Nov 2004
- Location
- Western NY
- Posts
- 946
maybe!!
it all depends on the piping, if the liquid and suction lines were sized to maintain refrigerant velocities during low loads then the separator is not needed.
is that a on-off system, no staging,unloading etc? where is the evaporator with relation to compressor?
-
05-08-2012, 02:35 PM #3
Professional Member
- Join Date
- Jan 2010
- Posts
- 4,410
valdelocc,
The only lines going up to the roof are the discharge lines from each compressor and then two liquid lines coming back from the air condenser on roof. The compressors are at the bottom of the air handler ( old Trane commercial ) with the evaporator just above. Very short suction lines about 3 feet. Two stage t-stat runs compressors.
-
05-08-2012, 03:41 PM #4
Regular Guest
- Join Date
- Nov 2004
- Location
- Western NY
- Posts
- 946
cant see why not
-
05-08-2012, 09:42 PM #5
Professional Member
- Join Date
- Jan 2010
- Posts
- 4,410
-
05-19-2012, 04:37 PM #6
Professional Member
- Join Date
- Dec 2004
- Posts
- 484
Are you sure its an oil seperator? Just a hunch but it might be a desuperheater that you are looking at
-
05-19-2012, 04:51 PM #7
Professional Member
- Join Date
- Jan 2010
- Posts
- 4,410
No I'm not. It has hot gas from the compressor going in then hot gas going out and a 1/4 line going back to the suction tube @ the compressor. All three lines come into the top. The flat top is bolted to the shell. I believe there is a core filter inside. Would a desuperheater look the same ?
-
05-19-2012, 05:26 PM #8
Professional Member
- Join Date
- Dec 2004
- Posts
- 484
What they might be doing is desuperheating the liquid to give you more usable btu's at the valve and then adding that absorbed heat back onto your suction line to boil off any liquid that night exist as a secondary percaution, which in essence is performing a very similiar function as if it was an accumilator.
I cant tell you 100% that is what you have or that you can get away without it but odds are you can do away with it without harming your equipment. What you will lose if efficenty and it will cost you more money to run and you will shorten the overall life of your compressor in the long term.
-
05-19-2012, 05:54 PM #9
Professional Member
- Join Date
- Jan 2010
- Posts
- 4,410
-
05-19-2012, 06:21 PM #10
Professional Member
- Join Date
- Dec 2004
- Posts
- 484
-
05-19-2012, 06:33 PM #11
Professional Member
- Join Date
- Jan 2010
- Posts
- 4,410
-
05-19-2012, 06:52 PM #12
Professional Member
- Join Date
- Dec 2004
- Posts
- 484
-
05-19-2012, 10:41 PM #13
Professional Member
- Join Date
- Jan 2010
- Posts
- 4,410
Well I just had to go and check it out. Here's what I found. Shell is 11" tall and 4" in diameter. Top is 3/8" solid copper with ten bolts to hold it down. Two 7/8" stubs one marked in one marked out. The 1/4" sae fitting marked oil. Removed top to find two mesh screens hang like lantern mantels. The 1/4" sae had a dip tube going to a 3" round ball float. Thanks for taking a shot at the title. Also was marked (Rightemp) the manufacturer I'm guessing.


Reply With Quote
I'll let you no what I find.