    Sisters ac unit, is this normal or what?

    she had a 3 ton 410 aruf goodman (not a hp) put in (meaning put in the central closet but not hooked up) this past february but wasnt charged up and running until her house was finished 2 weeks ago.

    When the thermostat clicks to turn the unit on, the air handler sounds like there is something else fairly quiet starting inside it for maybe 2 seconds then the blower fan will start up. That normal or what could that be?

    Then when the unit shuts off you can hear a gas hissing sound for maybe 5 seconds and the blower fan slowing down until it stops. That normal or what is that?

    Other than that the unit cools and runs perfectly and is very quiet, 20-22 degree difference between what comes out the closest ceiling vent and what goes in the supply grill and strong air flow out the vents.

    Told her i would post here for some opinions before she got the installing company out to ask the questions.

  2. #2
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    68,058
    Probably hearing the refrigerant starting to flow before the fan starts. And then equalize after the blower shuts off. Normal on many systems.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  3. #3
    Join Date
    Dec 2002
    Location
    Toledo, Ohio, United States
    Posts
    12,911
    Twilly says that is a good sound.
    No Heat No Cool You need Action Fast

  4. #4
    Join Date
    Jul 2004
    Location
    Massachusetts
    Posts
    6,837
    There's a short delay before the blower comes on. That's normal with the Goodman air handler. The hissing at the end of the cycle is the normal movement of refrigerant through the system as the high and low side pressures begin to equalize. Refrigerant just likes to move a lot and will continue even with the system off, constantly migrating from warmer to cooler areas. You just don't hear it unless it's moving under high pressure, which it is at the end of a cycle.
    If YOU want change, YOU have to first change.

    If you are waiting for the 'other guy' to change first, just remember, you're the 'other guy's' other guy. To continue to expect real change when you keep acting the same way as always, is folly. Won't happen. Real change will only happen when a majority of the people change the way they vote!

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event