Blower Cuts Out In Cooling
Carrier 48TFE012-A-611 ser 1004G50704
This unit will run for about 1 minute normally and then the blower will cut out. The contactor for the blower motor has 27 volts at the coil until it cuts out. Then it shows no low voltage. The compressors and condenser fan motors will continue to run until the unit cuts out on low pressure. The blower will not come back on until you cut power to it from the disconnect and then reestablish power. It looks like to me, the only thing that could cause this condition is a bad board. I haven't seen this before and was hoping that one of you have. If you need all of the gauge readings and etc, I have them but I didn't post them since I don't think they are relevant to the problem. Thanks in advance!
-
05-17-2012, 10:04 PM #2
Professional Member
- Join Date
- Jun 2008
- Location
- Rochester, NY
- Posts
- 61
Are you losing voltage at G when the blower cuts out?
The only advice I could give without being there is just look at the wiring diagram and trace back what's providing 24 volts to the coil.
-
05-17-2012, 10:09 PM #3
Professional Member
- Join Date
- Jun 2008
- Location
- Rochester, NY
- Posts
- 61
Nevermind that question...Forgot you need 24 volts to G on a carrier for the compressor to start.
-
05-17-2012, 10:09 PM #4
Does that unit have the fan contactor/ timer assembly. It just a fan relay with a small board
attached to it.
If it does or it gets it out put from a board jump the fsn coil wire to R to keep it running and then monitor the out put at the board.
Not much to those Carrier RTUs.
-
05-17-2012, 10:28 PM #5
Professional Member*
- Join Date
- Jan 2008
- Location
- Dallas ,Texas
- Posts
- 3,508
Go to the economiser board if it has the 4 LED`s on it and bypass the G terminal so the board doesn`t control the fan. Then look for corrosion on it. Change as neccessary.
UA 100
It takes three people to do anything around here. Two do the work, one explains to the crowd of people who showed up when they seen smoke and flames.
-
05-17-2012, 11:08 PM #6
Professional Member
- Join Date
- Jan 2010
- Posts
- 4,410
Check the fan logic for power in and out also the blower relay. Check t-stat as well.
-
05-18-2012, 08:39 AM #7
Professional Member*
- Join Date
- Mar 2010
- Location
- Arnold, Mo
- Posts
- 283
Thanks for the replies. I'm going back today so I'll let you know if your suggestions worked.
-
05-20-2012, 06:53 AM #8
What did you find.
-
05-20-2012, 04:23 PM #9
Professional Member*
- Join Date
- Mar 2010
- Location
- Arnold, Mo
- Posts
- 283
Sorry that it took me so long to reply. When I arrived back on the scene the unit had new problems. Blower still was not running but now the reset button on the economizer was tripped. I reset it and the unit cycled off on high pressure. I found that 1 of the 2 condenser motors is bad. I replaced the motor and dual capacitor (10/10 mfd) on Friday. With the economizer reset and the new condenser motor, it seemed to operate fine. I waited for about 30 minutes and then I split. I am going back this afternoon to check on it again (and drop the bill off). Even if everything is fine, I am still concerned with the economizer reset being tripped. I will keep you posted.
P.S. Something else that I found was that someone jumped out the board where the 5V fuse is supposed to be so there must have been a low voltage problem before me.
-
05-20-2012, 04:34 PM #10
Professional Member
- Join Date
- Jan 2010
- Posts
- 4,410
-
05-20-2012, 04:45 PM #11
Professional Member*
- Join Date
- Mar 2010
- Location
- Arnold, Mo
- Posts
- 283
-
05-21-2012, 12:43 AM #12
Professional Member
- Join Date
- Jan 2010
- Posts
- 4,410
-
05-21-2012, 06:29 AM #13[Avatar photo from a Florida training accident. Everyone walked away.]