    Blower Cuts Out In Cooling

    Carrier 48TFE012-A-611 ser 1004G50704
    This unit will run for about 1 minute normally and then the blower will cut out. The contactor for the blower motor has 27 volts at the coil until it cuts out. Then it shows no low voltage. The compressors and condenser fan motors will continue to run until the unit cuts out on low pressure. The blower will not come back on until you cut power to it from the disconnect and then reestablish power. It looks like to me, the only thing that could cause this condition is a bad board. I haven't seen this before and was hoping that one of you have. If you need all of the gauge readings and etc, I have them but I didn't post them since I don't think they are relevant to the problem. Thanks in advance!

  2. #2
    Join Date
    Jun 2008
    Location
    Rochester, NY
    Posts
    61
    Are you losing voltage at G when the blower cuts out?

    The only advice I could give without being there is just look at the wiring diagram and trace back what's providing 24 volts to the coil.

  3. #3
    Join Date
    Jun 2008
    Location
    Rochester, NY
    Posts
    61
    Nevermind that question...Forgot you need 24 volts to G on a carrier for the compressor to start.

  4. #4
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    18,804
    Quote Originally Posted by pvc1984 View Post
    Nevermind that question...Forgot you need 24 volts to G on a carrier for the compressor to start.
    That must be a Resi thing. Not true on the RTU's.
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist

    AOP Forum Rules:







  5. #5
    Join Date
    Nov 2004
    Location
    up in the hizzy
    Posts
    1,390
    Quote Originally Posted by timebuilder View Post
    That must be a Resi thing. Not true on the RTU's.
    some Carrier RTU's do need 24v at G for the compressor to run, I've worked in a few of them.

  6. #6
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    18,804
    Quote Originally Posted by valdelocc View Post
    some Carrier RTU's do need 24v at G for the compressor to run, I've worked in a few of them.
    Post a model # when you have a chance. I've never seen one.
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist

    AOP Forum Rules:







  7. #7
    Join Date
    Jan 2010
    Posts
    6,379
    Quote Originally Posted by valdelocc View Post
    some Carrier RTU's do need 24v at G for the compressor to run, I've worked in a few of them.
    So if you were to set the t-stat to fan on the compressor will start ?
    Or are you saying Y & G at stat ?

  8. #8
    Join Date
    Nov 2004
    Location
    up in the hizzy
    Posts
    1,390
    Quote Originally Posted by VTP99 View Post
    So if you were to set the t-stat to fan on the compressor will start ?
    Or are you saying Y & G at stat ?
    nope mechanical cooling control interlocked with fan contractor, very simple stuff! sooner or later you'd run into one.

  9. #9
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    68,314
    Quote Originally Posted by VTP99 View Post
    So if you were to set the t-stat to fan on the compressor will start ?
    Or are you saying Y & G at stat ?
    If you jumper R to Y at the board of the RTU. The compressor won't run, unless the blower contactor is in also.

    First time you run into one, it throws you off.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  10. #10
    Join Date
    Apr 2012
    Location
    Paper Street Soap Company
    Posts
    2,304
    Quote Originally Posted by flanders View Post
    Carrier 48TFE012-A-611 ser 1004G50704
    This unit will run for about 1 minute normally and then the blower will cut out. The contactor for the blower motor has 27 volts at the coil until it cuts out. Then it shows no low voltage. The compressors and condenser fan motors will continue to run until the unit cuts out on low pressure. The blower will not come back on until you cut power to it from the disconnect and then reestablish power. It looks like to me, the only thing that could cause this condition is a bad board. I haven't seen this before and was hoping that one of you have. If you need all of the gauge readings and etc, I have them but I didn't post them since I don't think they are relevant to the problem. Thanks in advance!

    Does that unit have the fan contactor/ timer assembly. It just a fan relay with a small board
    attached to it.

    If it does or it gets it out put from a board jump the fsn coil wire to R to keep it running and then monitor the out put at the board.

    Not much to those Carrier RTUs.

  11. #11
    Join Date
    Jan 2008
    Location
    Dallas ,Texas
    Posts
    3,723
    Go to the economiser board if it has the 4 LED`s on it and bypass the G terminal so the board doesn`t control the fan. Then look for corrosion on it. Change as neccessary.
    UA 100

    It takes three people to do anything around here. Two do the work, one explains to the crowd of people who showed up when they seen smoke and flames.

  12. #12
    Join Date
    Jan 2010
    Posts
    6,379
    Check the fan logic for power in and out also the blower relay. Check t-stat as well.

  13. #13
    Join Date
    Mar 2010
    Location
    Arnold, Mo
    Posts
    441
    Thanks for the replies. I'm going back today so I'll let you know if your suggestions worked.

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event