    Anyone have issues with the testo 550 temp clamps not being accurate in package units seems like they not well insulated from airflow

  2. #2
    Join Date
    Nov 2001
    Location
    east kansas
    Posts
    8,033
    I've had doubts also.
    Beware of advice given by some guy on the Internet.

  3. #3
    Join Date
    Aug 2004
    Location
    North Richland Hills, Texas
    Posts
    14,915
    The sensors themselves are very accurate.

    The problem is that to get precise readings, the sensor needs to be making good contact with the pipe along the full length of the sensor barrel, and if there is more than a few degrees temperature difference between the pipe and the ambient air, you need to insulate it.
    If more government is the answer, then it's a really stupid question.

  4. #4
    Join Date
    Jan 2005
    Location
    Akron
    Posts
    1,170
    This is an interesting questions as there are many factors to consider.

    First, the sensor is not more affected by the ambient air than the uninsulated pipe itself. If the pipe is exposed to ambient air it is absorbing heat also. When the fan starts the temperature of the pipe will change if there is only vapor in the line. Any uninsulated suction line should be insulated all the way back to the compressor. Any heat picked up in the suction line has to be rejected by the condenser reducing capacity, plus it reduces the cooling to the compressor.

    Second, air is considered an insulator (if it is not moving) Shielding the clamp from the wind would be more important than insulating it from ambient temperatures.

    Third, the exterior of the pipe is never the same as the temperature of the refrigerant flowing through it. I have tested several pipe clamp designs and found the best clamps are typically within 1 degree of the saturation temperature of the refrigerant. BTW, Testo and Digi-Cool use the most accurate sensors. I have tested them both. They are typically within .9 degrees of the saturation temperature.

    Position of the probe affects the readings. Just like clock position of a TXV sensing bulb, a temperature sensor should be positioned the same way. I have a clamp probe tester that I built, and even on a 1/2" line there is a temperature gradient between the top and bottom of the line. If you look closely at the end of the sensor, that is the coldest are as the clamp is insulating the pipe from the wind.

    Radiant heat could influence the reading. I have never understood why we do not make white Armaflex. I have found the clamp probe to be minimally influenced by solar gain.

    The sensor mount can affect the accuracy. Testo has temperature compensation built into the Testo 570 for additional accuracy.

    Last, because you are using the value to calculate superheat and sub-cooling you have to consider the total uncertainty of the instrument. The pressure reading will be converted to a saturation temperature. Any inaccuracies in the pressure measurement will also affect the calculation. If you leave refrigerant liquid in your hoses, clamp the probe to the hose and let it sit, the pressure in the hose will correspond to the saturation temperature of the refrigerant which should correspond to the temperature of the probes. I do this all the time for a quick check of the refrigerant and the refrigerant purity before hooking up gauges to a new system.

    Testo uses atmospheric pressure (manual setting in the 550, and automatic in the 557 and 570). Digi-Cool can be adjusted in a vacuum. All manufactures of gauges today use relative sensors. If there is no way to compensate for the effects of atmospheric pressure the superheat and sub-cooling calculations will also be negatively impacted.

    But to answer your question, I have found the effects to be very small as the pipe is a much better conductor of heat to the sensor than air to the sensor. The majority of the sensor is in contact with the pipe of the plastic insulator that it is housed in.

    I attached a thermal image of a Testo clamp probe strapped to a pipe. You can see that the sensor is very close the the pipe surface temperature. If we were to blow air on the assembly, the temperature of the entire assembly would be affected.
    Attached Images Attached Images  
    JLB,

  5. #5
    Join Date
    Oct 2006
    Location
    tx
    Posts
    26
    Good info Jim I feel more confident in trusting its readings just have to make sure clamp is on pipe correctly and let 550 do the rest

  6. #6
    Join Date
    Jan 2005
    Location
    Akron
    Posts
    1,170
    I shot a couple of videos that you might find interesting on clamp probe accuracy.

    http://youtu.be/k9LXhw8WVU0

    http://youtu.be/1Llh4PaaGnI

    http://youtu.be/mtsQ2X07f0A
    JLB,

  7. #7
    Join Date
    Mar 2007
    Location
    wedged in freezer shelf
    Posts
    6,961
    Nice video Jim. You up for placing the temp. sensor directly to the pipe wrap some tin foil around the sensor and pipe then wrap insulation over the whole thing?
    Copper conducts very well IMO and I have seen numbers matching up under saturated conditions with different meters and sensors (523 and 1250)
    I believe you might see the same.
    “If You Can Dodge A Wrench You Can Dodge A Ball”

  8. #8
    Join Date
    Jan 2005
    Location
    Akron
    Posts
    1,170
    Quote Originally Posted by itsiceman View Post
    Nice video Jim. You up for placing the temp. sensor directly to the pipe wrap some tin foil around the sensor and pipe then wrap insulation over the whole thing?
    Copper conducts very well IMO and I have seen numbers matching up under saturated conditions with different meters and sensors (523 and 1250)
    I believe you might see the same.
    Sure, I can shoot that tomorrow. I have some heat sink compound also I can add to the mix. Considering however that it takes about 2 seconds to install the clamp, I could live with 0.7 to 1.5 degrees. I will try your suggestion though, it will be interesting.
    JLB,

  9. #9
    Join Date
    Mar 2007
    Location
    wedged in freezer shelf
    Posts
    6,961
    You would need a little more time rigging up the clamp to work in a package unit like the OP noted
    “If You Can Dodge A Wrench You Can Dodge A Ball”

  10. #10
    Join Date
    Jan 2005
    Location
    Akron
    Posts
    1,170
    Ice,
    Here you go.

    http://youtu.be/B9cyDrQ3xTU
    JLB,

  11. #11
    Join Date
    Mar 2007
    Location
    wedged in freezer shelf
    Posts
    6,961
    looks good bro
    the tin foil was for under the ins. though lol
    it carries the temp of the pipe up and around the hole barrel and will give you a quicker response to temp changes
    “If You Can Dodge A Wrench You Can Dodge A Ball”

  12. #12
    Join Date
    Feb 2010
    Location
    In a boiler room
    Posts
    7,158
    Very good illustration Jim!

    It is interesting that a temp clamp can be over 1° off in a 78° room. I wonder how far off it would be on a 90° roof in direct sunlight while clamped on a 45° suction line?

  13. #13
    Join Date
    Jan 2005
    Location
    Akron
    Posts
    1,170
    The way that the testo clamps are made with the foot that is separate from the clamp body, I am guessing not a lot different. If stuck in direct sunlight though a piece of tin foil over the clamp might really help with additional accuracy.
    JLB,

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event