Scroll running backward
No cooling call. A new 3 phase Carier Rtu that was installed in winter. 4 ton scroll. Installing contractor MIA. It Never ran in cooling until today. It ran backwards for about 6 hours im guessing. Comp was off on IO I let it cool, reversed leads and everything was normal. What can be expected for the future of this unit?
-
05-16-2012, 09:27 PM #2
-
05-16-2012, 09:31 PM #3
Usually they heat up and trip the internal overload , reset and the do it all over again.
Im guessing this thing is under warranty ? Ask the customer if they want to swap out the comp. If they will pay labor that is.
Reaaly I thinks its probably fine. I had a data aire that ran backwards for two days. That was 3 years ago. and its still running.
-
05-16-2012, 09:36 PM #4
Professional Member
- Join Date
- Jun 2008
- Location
- Rochester, NY
- Posts
- 61
I would've checked pressures, temperatures, ohmed out the compressor, and recorded amp draws on my paperwork. Record everything to CYA!! If all that checked out and the compressor sounded okay, just hope for the best....that's all you can do really.
-
05-16-2012, 09:40 PM #5
Professional Member
- Join Date
- Jun 2008
- Location
- Rochester, NY
- Posts
- 61
-
05-16-2012, 10:01 PM #6
Professional Member*
- Join Date
- Jan 2008
- Location
- Dallas ,Texas
- Posts
- 3,506
-
05-17-2012, 12:04 PM #7
Regular Guest
- Join Date
- Feb 2012
- Location
- central Florida
- Posts
- 96
Good advice document your work so it does not come back to bite you later. that has saved me on several occasions.They cannot say you were at fault that way and believe me they will.
-
05-17-2012, 07:02 PM #8
Professional Member
- Join Date
- Sep 2006
- Location
- Ohio
- Posts
- 343
So was the blower also running backwards or was the compressor wired wrong from the factory?
-
05-17-2012, 07:05 PM #9"The problem is the average person isn’t tuned in to lifelong learning, or going to seminars and so forth. If the information is not on television, and it’s not in the movies they watch, and it’s not in the few books that they buy, they don’t get it" - Jack Canfield
-
05-17-2012, 08:09 PM #10
-
05-17-2012, 10:20 PM #11
Professional Member
- Join Date
- Jun 2008
- Location
- Rochester, NY
- Posts
- 61
Don't get me wrong...I agree with you 100%. I would take care of the customer anyway I could and definitely do what I can.
This thread also reminds me...on new Carriers....make sure and look at the voltage ratings on the blower motor. Already seen it a couple times where they put a 208 volt motor in a 460 volt unit. The motor doesn't usually last long lol.
-
05-18-2012, 04:03 PM #12
Professional Member
- Join Date
- Sep 2006
- Location
- River Forest IL
- Posts
- 70
Something to consider-
If you have a unit that has 3 phase compressors and blower motor, they should both be phased properly from the factory (A-B-C). That doesn't mean they can't be wired wrong in the field, but if one is running backwards, they both should be. (though "should" doesn't mean "always is the case") Maybe when they started it up it in the field it was too cold to start up cooling, and the compressor was phased wrong at the factory-maybe they meant to do a cooling startup when conditions were better, and would certainly have caught it then.
If the compressor is 3 phase and the blower is single, it's still possible that the compressor was started up and running in the right rotation at one point, but if someone changed the contactor and accidentally crossed up the wiring, that would reverse rotation also.
Not to mention: there could have been a phase reversal at the pole, coming into the building (though that would affect all 3 phase motors from that feed), the panel could have been changed, and that breaker had wiring crossed.
All I'm really getting at is just because we run into equipment running backwards, doesn't mean it was always running backwards...things happen. Sometimes equipment gets started up correctly, and outside forces change things.
And....sometimes folks just hit the go button, hope for the best, and head for the bar.
-