when checking the superheat at the compressor with a accumulator do you still check the superheat 6 inches from the compressor or do you have to be before the accumulator to get a proper reading
-
06-29-2006, 09:01 PM #2
Here's my take
Temperature and pressure are directly related. Accumulators to not reduce pressure, just convert liquid to gas.
Take the reading 6" before the compressor.
06-29-2006, 09:33 PM #3
Professional Member
- Join Date
- Mar 2004
- Location
- New England
- Posts
- 224
When looking at compressor super heat We are looking at being in the area above flood back or known as 0 super heat and below maxium rated superheat of the compressor.Accumulators sized incorrectly will not prevent flood back, measure at the compressor.A lot of field installed accumulators are sized by line connections and not by the amount of refrigerate in the system.
An apprentice is half a journeyman ,two apprentices is a call back.
06-30-2006, 11:50 AM #4
Professional Member
- Join Date
- Aug 2002
- Posts
- 6,047
Ja, you should get an award or something!!!
So many dont even ask that question, much less do they EVER measure superheat back @ the compressor!
They simply go by hi and lo side pressures to charge or diagnose systems.
pity.........
06-30-2006, 05:26 PM #5
Professional Member
- Join Date
- Apr 2006
- Location
- new york
- Posts
- 101
thanks for the replies it very appriciated
07-12-2006, 10:44 PM #6
Regular Guest
- Join Date
- Jul 2006
- Posts
- 11
to ensure comp wont flood back check 6" by comp but to setup a txv check as close to sensng bulb as possible to get most accurate temp reading. txv does not care what superheat is at comp